    PLEASE Help with a Daikin VRV_II Compressor Phenom



    I'm hoping those in the UK with more experience with Daikin than us on this side of the pond can help us. We've got a Daikin VRV_II condenser that seems to be getting hot gas back to the compressor somehow. We've replaced the 4-way valve twice. The guy that replaced it the first time didn't use a heat sync and totally melted the plastic actuator inside. We've done a proper replacement on the 4-way valve but we have to run the unit on the standard compressor only. For some reason the inverter compressor is getting a tremendous amount of hot gas back in and it gets dangerously hot very very fast. I must add that the guys who did the original install were crap and the machine has never really worked right. Can anyone offer input for the cause of this?? PLEASE HELP. Cheers.



  2. #2
    mitchilin's Avatar
    mitchilin Guest

    Re: PLEASE Help with a Daikin VRV_II Compressor Phenom

    hi,vrv 2 normal cooling operation condenser solenoid valve Discharge gas pipe y5s turned off,detect pipe temperature to see if valve stuk open.the same with solenoid valve High pressure y7s turned off , detect pipe temperature to see if valve stuk open.i have same problem and found discharge mechanichal valve stuk open.change valve.good look.

  3. #3
    Join Date
    Jul 2009
    Location
    United States
    Posts
    9
    Rep Power
    0

    Re: PLEASE Help with a Daikin VRV_II Compressor Phenom

    Thank you very much for the reply. I tested this out today and unfortunately the valve seems to be closed. i was hoping this would fix the issue. Thanks anyways. We're still working through it.

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: PLEASE Help with a Daikin VRV_II Compressor Phenom

    Possible restricted suction strainer at the Y junction so the hot gas injection valve is energised

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin FDYQ250M
    By carl in forum Air Conditioning
    Replies: 7
    Last Post: 11-08-2009, 12:56 AM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •