    How much to run an 15kw a/c system



    Hi,
    I am interested to find out the equation to work out how much it costs to run electrical equipment.

    The particular unit i'm interested in is a mitsi 15 kw cassette.

    I want to assess the cost of a both a 3 phase and single phase system when the system is running, also i'd like to to know the generally assumed average running time per hour for a properly sized A/C motor.

    Shall we take the supplies as 415v and 230v respectively use the standard powerfactor and the unit price per kwh as £0.10

    A woman told me today that the unit in question cost there organisation £60,000 a year to run and i'd love to stick a properly worked equation under her nose or up it.

    Regards Steve
    Last edited by get the gauges; 12-08-2009 at 07:21 PM.


    Put the screwdriver down and step away from the expansion valve !!!! OK Gary i won't touch it unless instructed.

  2. #2
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: How much to run an 15kw a/c system

    Quote Originally Posted by get the gauges View Post

    A woman told me today that the unit in question cost there organisation £60,000 a year to run and i'd love to stick a properly worked equation under her nose or up it.

    Regards Steve

    She might be right if shes inclueing maintenance from some of the cowboys.....

  3. #3
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: How much to run an 15kw a/c system

    Try the LG one or ask Mitsi themselves. Space also have a cost calculator too

    http://www.mylg.co.uk/

  4. #4
    Join Date
    Oct 2007
    Location
    w.mids
    Age
    49
    Posts
    110
    Rep Power
    17

    Re: How much to run an 15kw a/c system

    Quote Originally Posted by multisync View Post
    Try the LG one or ask Mitsi themselves. Space also have a cost calculator too

    http://www.mylg.co.uk/

    Hey thanks,
    I used that and came up with a £1072 for 52 weeks of use. I looked up a mitsi 3phase 14.5 kw unit and found the nominal kw input to be 4.36.

    What do you reckon, worked it out in my head to be 3k if the comp never stopped so a system that starts and stops as it should properly would be about that i reckon.

    Thanks Steve
    Put the screwdriver down and step away from the expansion valve !!!! OK Gary i won't touch it unless instructed.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Ammonia Heat Pumps
    By US Iceman in forum New Technologies
    Replies: 39
    Last Post: 22-03-2010, 06:36 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •