    VRV oil return issue



    dear sirs

    If the evapoator is much lower than compressor(I've read the distance can be more than 50m), how VRV system deal with the oil return issue? adding the U bend every 10m height or other ways?


    regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: VRV oil return issue

    Quote Originally Posted by Lc_shi View Post
    dear sirs

    If the evapoator is much lower than compressor(I've read the distance can be more than 50m), how VRV system deal with the oil return issue? adding the U bend every 10m height or other ways?


    regards
    LC

    No they do not trap pipes.

    The runs are sized to allow the correct flow and there are regular gas flushes to push the oil back.

    Cheers taz.


    .

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: VRV oil return issue

    Hi taz

    You mean that the proper gas velocity can bring back the oil to compressor. Is it necessary to apply oil separator at the discharge ?

    thx & regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: VRV oil return issue

    VRV & VRF systems have oil seperators which are very efficient & return most discharge oil straight back to the compressor so only a very very small volume of oil gets to circulate through the system.
    but
    The outdoor unit has to be able to cope with low load / slow compressor speed for long periods of time.
    Different manufacturers have different control stratagy to cope with is operating condition.

    VRV systems for many years had fixed oil recovery mode after a fixed number of operating hours. Later models have operating conditions compensated time period for oil return mode.
    The oil return mode ensures that any small volume of oil which gets through the oil seperator will be returned to the compressor at the latest by the oil return mode.
    The operation & compressor speed is dictated by the oil return control stratagy during oil return mode to ensure refrigerant velocity is high enough to force oil to return to outdoor unit & compressor.

    For many VRV / VRF systems oil traps on risers not required due to this control stratagy provided the correct pipe sizes have been installed.

    Cheap copies of the Japan VRV / VRF systems have been noted to take short cuts to make equipment cheaper but this is one area where short cuts are not a good idea.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: VRV oil return issue

    What I heard Lc is that they open on a regular base all the EEV's at once with a low SH so that max speed is achieved in the lines.
    Low SH to flush out the oil. The liquid separator prevents eventual liquid slugging.
    We do it also this way on packs with long lines.
    If you look once to AC lines, they're always calculated with high to very high speed.
    I suppose they select rather on a 1K pressure drop over the line then on a certain speed.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: VRV oil return issue

    What is a VRV VRF , is it some type of variable speed drive ?

    Sorry off the subject .

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: VRV oil return issue

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. McQuay ALS F XE273.2 990Kw, highest return temp?
    By THE WOMBAT in forum Technical Speculations
    Replies: 1
    Last Post: 07-08-2009, 10:59 AM
  2. Best place for return air sensors, in the room or ceiling void?
    By back2space in forum Air Conditioning
    Replies: 27
    Last Post: 06-07-2009, 06:21 AM
  3. Flood back issue?
    By Arc in forum Trouble Shooting
    Replies: 15
    Last Post: 28-10-2008, 04:40 PM
  4. Oil Return On Dx Systems
    By AYIBIBIO in forum Heat Pumps
    Replies: 0
    Last Post: 10-02-2008, 10:26 PM
  5. return air
    By subzero*psia in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2001, 04:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •