    Question Does EPR rises Compressor capacity???



    Hello everybody!

    I'm in a dilemma... I'v being designing systems for Commercial Refrigeration for 2 years, but now talking to an Engineer in a Convention I assited a week ago, we discussed the way to select compressors in a parallel system where different evaporation temperatures are present (Different rooms, different emps). We both use EPR valves so the compressors will work at the same inlet pressure, but the dilemma comes when he tells me he uses a "factor" to rise the calculated capacity of the compressors proportional to the differential of the pressure before and after the EPR in the circuits where temperature are higher, in other words: he says that if a EPR is used in parallel systems, compressors should be calculated using a "factor" that rises their capacity...

    Have you hear something like this before??????

    Thanks in advanced!



  2. #2
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Does EPR rises Compressor capacity???

    Ok guys, those who didn't understand the question please say I.... jejeje......

    Seriously, nobody has heard about this at all????

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Does EPR rises Compressor capacity???

    The use of EPR's determines what the lowest suction pressure is for the compressor. Whatever the lowest evaporating temperature is the compressor has to meet this + all other loads. One thing that is sometimes forgotten is the compressor has to meet all loads at the lowest pressure because the other loads are operating at a higher temperature/pressure and open to the lowest pressure in the suction line.

    What it sounds like he is doing is adding a correction factor to say: when the lowest temperature load is off the rest of the evaporators are operating at higher suciton pressures so you might as well raise the suction pressure to match the loads. Doing this might increase the heat rejection to the condenser since the compressor capacity is now higher.
    If all else fails, ask for help.


  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Does EPR rises Compressor capacity???

    If total load is required, then compressor must match this loead st the lowest SST. If the loads are split and happen at different times, then you need to calculate using 2 different compressor configurations.
    If the system is a combination, then you can use a floating suction set point. ( for efficiency)
    For example if the LT system is controlled by a liquid solenoid valve, and comp(s) load/unloading is by suction set point, then the set point can be raised when LT is not in use allowing the compressor to unload and reducing power draw, increasing efficiency

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Does EPR rises Compressor capacity???

    To calculate load of comp you should go for lowest suction pressure and if your using EPR's do not forget two thing 1- put check valve on suction pipe of rooms has a high temperature than lowest room temperature and also check rang of comp in suction pressure it can work if it can not work , you have to putCPR ( Crankcase Regulator pressure ) for them to protect your comp fficeffice" />>>
    >>
    pressure to match the loads. Doing this might increase the heat rejection to the condenser since the compressor capacity is now higher

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Does EPR rises Compressor capacity???

    Hi Guys,

    My opinion is the following...see the file. This justify the increasing of capacity. R404A as example and no superheat has been considered just for simplicity.

    Sandro
    Attached Files Attached Files
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Does EPR rises Compressor capacity???

    Simple answer. Efficiency. Buy a screw on a vsd with a different machine for each system then have them properly commissioned with a full cop result and proof of capacity test done at the end. Bigger install cost but it will pay for it's self in a few years.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

  8. #8
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Does EPR rises Compressor capacity???

    Thanks to all.

    Sandro:
    could you explain me a little more about your answer, I really don't understand the increase of capacity you show on the diagram.

    Thanks!!!

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Does EPR rises Compressor capacity???

    Quote Originally Posted by georgedvf View Post
    Thanks to all.

    Sandro:
    could you explain me a little more about your answer, I really don't understand the increase of capacity you show on the diagram.

    Thanks!!!
    Geogedvf,

    The difference of enthaply between +45ºC and -5ºC will be bigger than +45ºC and -30ºC. If you have refrigerated stores at +2ºC DT=7ºC, for example, the compressor (at -30ºC) will give more capacity due to the increased superheat. Of course the specif volume will increase but for R404A/R507 the final effect is still a little increase of capacity.


    Sandro
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Does EPR rises Compressor capacity???

    Quote Originally Posted by Sandro Baptista View Post
    Geogedvf,

    The difference of enthaply between +45ºC and -5ºC will be bigger than +45ºC and -30ºC. If you have refrigerated stores at +2ºC DT=7ºC, for example, the compressor (at -30ºC) will give more capacity due to the increased superheat. Of course the specif volume will increase but for R404A/R507 the final effect is still a little increase of capacity.


    Sandro
    Sandro,

    I have the idea that the difference of enthalpy shown in the diagram means the evaporating capacity of the system, but not for the compressor capacity.

    Why do you say that the difference of enthalpy is the compressor capacity?

    Also, if you go to the manufacturer's capacity tables for compresors you will see that at +45ºC and -5ºC a compressor has more capacity than at +45ºC and -30ºC.

    If I'm wrong, please correct me

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Does EPR rises Compressor capacity???

    thumb rule : LOAD ON THE LOWEST TEMPERATURE EVAPORATOR SHOULD NOT BE LESS THAN 60% PREFERABLY MORE OF THE TOTAL LOAD . AND LOW TEMP EVAPORATOR SHOULD HAVE NRV IN SUCTION LINES ( AT THE OUTLET OF THE EVAP)

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Does EPR rises Compressor capacity???

    Quote Originally Posted by georgedvf View Post
    Sandro,

    I have the idea that the difference of enthalpy shown in the diagram means the evaporating capacity of the system, but not for the compressor capacity.

    Why do you say that the difference of enthalpy is the compressor capacity?

    Also, if you go to the manufacturer's capacity tables for compresors you will see that at +45ºC and -5ºC a compressor has more capacity than at +45ºC and -30ºC.

    If I'm wrong, please correct me

    georgedvf,

    The difference of enthalpy that is hatched means the increase of capacity that the compressor will have due the fact the system can take chance of the extra superheat at the suction compressor.

    Sorry, but on the previous emails I never saida that a compressor at -5ºC gives less capacity than at -30ºC. Sorry if I didn't explain too well.
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Does EPR rises Compressor capacity???

    Quote Originally Posted by D.D.KORANNE View Post
    thumb rule : LOAD ON THE LOWEST TEMPERATURE EVAPORATOR SHOULD NOT BE LESS THAN 60% PREFERABLY MORE OF THE TOTAL LOAD . AND LOW TEMP EVAPORATOR SHOULD HAVE NRV IN SUCTION LINES ( AT THE OUTLET OF THE EVAP)
    Koranne,

    My opinion is if the low temperature aircoolers demand a great part of cooling capacity on the compressor and / or if the compressor can pull down well the suction pressure to low temperature regime (to temperatures below the cold stores temperatures, is enough) then no need of check valves (they represent a source of suction head loss).
    To make progress is never good enough, I want to do better and better and better