    Kiour controller problem ?



    Hi i have a MPS fridge with the Kiour REF DF controller.
    Lately it keeps going to minus 6 deg C. If i give the front of the controller a good hardish tap it will return to normal function. But it keeps doing this quite often now.

    Should I buy a new control unit ? or is there another way to fix this ?
    If i buy a new controller is it a basic swap job. take old one out put new one in with the wires going in same position.

    thanks.



  2. #2
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Kiour controller problem ?

    i am not familiar with the fridge or controller.generally this comes about when the relay contacts for the compressor wear from arcing and have a habit of sticking together,generally because of not being rated to compressor(undersized contacts) or short cycling.if you locate the relay on the board thats suspect you may be able to replace it.apart from that fitting of new controller with a slave relay with balls to switch the compressor is the way to go.check board for dry joints and loose connections also.if buying a new controller get the same model and work it from their
    mmm to beer or not to beer...........lets drink breakfast

  3. #3
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Kiour controller problem ?

    kiour controllers are well known for the relays to stick not very reliable in my experience.
    i would replace it with an id chill controller personally

  4. #4
    Join Date
    Jul 2008
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: Kiour controller problem ?

    KIOUR
    Type REF-DF. Model REF-DF-SM. V2.0
    Refrigeration temperature controller with dFrost. Type REF-DF. Range -19 - +99 °C/°
    F

    General characteristics.
    Electronic controller
    REF-DF is a compact unit for refrigerator’s control with dFrost control. It is provided with 3 relays, compressor (30 A),
    water level control and ON-OFF relay. In the
    OFF state all relays are OFF and is displayed OF. Inputs: one PTC temperature sensor and one water
    level control. Range: -19 °C - +99 °C/°F. Resolution one unit. Accuracy: 0,5 %. ±1 digit.

    Managing the unit
    df :
    By pressing df button continually for 5 sec, a dFrost cycle is forced.
    :By pressing this button for 3 sec the state changes from
    OFF to ON or from ON to OFF. For 1 sec the setup °C or °F is displayed.

    Managing the parameters
    1)
    By pressing button the parameter SP (Set Point) and its value is displayed.
    By pressing at the same time the
    button and the up or down arrow, the value is changed.
    2
    ) By pressing at the same time the up and down arrows and the SET button the menu of the parameters and the first
    parameter
    SP is displayed.
    By pressing the down arrow we can see the other parameters as they appear in the table below. By pressing
    SET the value
    of the parameter is displayed and with the arrows the value can change.
    By pressing
    button we confirm the new value and the name of the parameter is displayed.
    By pressing
    SET we cancel the new value and the name of the parameter is displayed.
    To exit the parameters, we press
    button.
    Serial input.
    Via serial input the instrument is connected to the memory backup (key) or to a network.
    1.
    Memory backup (key): With the key we can save the setup of the parameters. Actions: Connect the key to the instrument.
    a. By pressing
    SET and the UP Button the instrument performs the connection to the key and the message Eo is displayed.
    b. By pressing
    UP Button the instrument reads the parameters from the key. Messages: ro = read O.K. , rF = read Fail.

    b. By pressing
    DOWN Button the instrument writes the parameters to the key. Messages: Yo = Write o.K. , YF = Write
    Fail.
    The key can be connected to various types of instruments. If you try to read the parameters of a different instrument,
    a message
    rF = read Fail is displayed.
    At all instruments and at any time we can perform the write operation. After 10 sec, the key is disconnected automatically.
    2.
    Connect to network: The instrument is connected to a network RS485 via an interface (modbus protocol). The computer controls the
    communication, receives data from the instrument and reads/writes the parameters. The maximum distance between the instrument and the
    computer is 1000 meters.

    A/A PARAMETERS - DESCRIPTION
    1 SP SET POINT
    temperature control room. Values: SL - SH.
    2 SL
    Lower limit adjusting temperature SET POINT. Values: -18 - 25 °C.
    3 SH
    Maximum limit adjusting temperature SET POINT. Values: 0 - 98 °C.
    4 di
    Differential working temperature of compressor. Values: 1 - 8 °C.
    5 Cr
    Minimum stop time of compressor. Values: 0 - 4 minutes.
    6 Cf
    Compressor working mode with sensor malfunction. Values: 0 and 1.
    Value 0 = 40% ON compressor. (3 minutes
    ΟΝ, 4 minutes OFF the compressor).
    Value 1 = 100% On compressor. (
    ΟΝ continually the compressor).
    7 dF
    Times of dFrost every 24 hours. Values: 0-12. 0= Not make dFrost.For example: Value =6. 24/6=4. Every 4 hours starts
    dFrost.

    8 dt
    Maximum duration of dFrost. Values 1 - 90 minutes.
    9 dL
    Temperature limit of dFrost. Values: 1 - +20 °C. Above this temperature the dFrost stops and it is not possible to start the
    procedure again manually.

    10 do
    Type of dFrost. Electrical. Fixed. Compressor OFF.

    11 dr
    Dripping Time. Value 0-10 minutes. Time OFF compressor after dFrost.

    12 td
    Message dF is displayed from the beginning of the dFrost until time expires. Values: 0 - 99 minutes.

    Value = 0, during dFrost the temperature of the room is displayed.
    13 AJ
    Zero adjustment of sensor. Values: -9 - 10 °C.
    14 ts
    Refresh delay of temperature indication at display. Values: 0 - 20 Sec.
    15 FC
    0 = °C. 1 = °F. ATTENTION. Changes between °C and °F do not effect the value of the parameters.(ex.SET POINT 10 °C is
    10
    °F )

    16 Br
    Baud Rate. (9600)

    17 tr t
    ime respond. The respond time of the instrument. Values in mSec. Default 20 mSec. Values 5 - 100 mSec.
    18 Ad
    Address of instrument at the network operation. Values 1 - 255
    Technical Specifications

    —Power supply: 230 or 115 VAC. After request.
    —Accuracy 0,5 % ±1 digit
    —Connection. TAB 6,3 mm.
    —Relay 250 VAC 30 A Resistive Load.
    —Relay 250 VAC 5 A Resistive Load.
    —Maximum power consumption: 3 Watt.
    —Working temperature: -10 - 60 °C.
    Storage temperature: -20 - +80.
    ATTENTION: It is necessary to prevent electrostatic discharges at the side ventilation openings.Also prevent insertion of pointed elements.

    Connection diagrams - Dimensions. Other Characteristics.
    Connection Diagram Front Panel Cut off Dimensions External Dimensions
    1 2 3 4 6
    N R
    7 8 9 10 11
    KIOUR
    REFRIGERATOR CONTROLLER
    Type REF-DF Model REF-DF-SM
    Range -19 - +99 C

  5. #5
    hamster's Avatar
    hamster Guest

    Re: Kiour controller problem ?

    Hi friging hell if i just replace the controller for a new one will i need all that information to set it ? Will it not be programmed from the factory ?

    thanks

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Kiour controller problem ?

    specs look pretty reasonable pity the thirty amps is rated at resistive loading,dont reckon ive come across one yet thats rated that high.

    ah yeah hamster
    yes you will
    no it wont
    anytime

    ps;small hint - write down original parameter settings in controller to put in new controller later.
    cheers buddy!
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    hamster's Avatar
    hamster Guest

    Re: Kiour controller problem ?

    What's this serial input thing ? Do you need some sort of device for this ? Seems like i would need a professional installation engineer.

  8. #8
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Kiour controller problem ?

    ignore the serial input thingy.if you write down the original controller parameters,then go to the place to purchase your controller,they should be able to programme the controller for you.i still advise a slave relay rated to correct conditions ie.inductive load,be fitted if you dont want this problem to recur.out of curiosity how long have you had this controller or fridge?
    mmm to beer or not to beer...........lets drink breakfast

  9. #9
    hamster's Avatar
    hamster Guest

    Re: Kiour controller problem ?

    I've had this fridge for 4/5 years. It first had this problem about a year ago and i just tapped it and that got it working but has this problem every now and then. I need to give it a fair good hit now to get it working properly now. If i hit it hard enough the condensor will stop running and stop freezing everything.

    I contacted MPS which is the brand of my fridge and they sell the controller for about 97 quid. and they say i dont need to programme it. should be easy enough to swap over. I will have to order one.

    sorry i dont have any clue about that slave relay, my electrical knowledge is very limited.

  10. #10
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Kiour controller problem ?

    Quote Originally Posted by hamster View Post
    I've had this fridge for 4/5 years.


    sorry i dont have any clue about that slave relay, my electrical knowledge is very limited.
    maybe buy two controllers as they wont be any cheaper in eight to ten years let alone availability

    the controller output for the condensing unit is utilised to power another relay(say 20 amps inductive load)incorporating a neutral.the condensing unit power is then fed from the relay contacts when power is applied from seperate source other than controller output.

    ie active from controller powers relay solenoid coil but needs a neutral.
    when energised it switches the relay contacts
    power is applied from a permanent source other than controller output,the contacts are closed and power is applied to both terminals the later being the original wire from the output of the controller.
    best get a fridgy in to do his as controller output maybe switching neutrals instead of actives.
    Last edited by lowcool; 12-08-2009 at 04:33 AM.
    mmm to beer or not to beer...........lets drink breakfast

  11. #11
    KIOUR's Avatar
    KIOUR Guest

    Re: Kiour controller problem ?

    Hello

    I have checked your problems with the relay. Because of voltage drops, more amperes from nominal current seep through the relay contact and melt it. The new version, REF-DF-SM has a stonger relay, 30A. You will not have any problems with this one. For further information please contact me at info@kiour.com.

    Best regards,
    Ino Kiourtsidou

    KIOUR

  12. #12
    KIOUR's Avatar
    KIOUR Guest

    Re: Kiour controller problem ?

    Hello

    I have checked your problems with the relay. Because of voltage drops more amperes from nominal current seep through the relay contact and melt it. The newer version REF-DF-SM has a stonger relay, 30A. You will not have any problems with this one. For further information please contact me at info@kiour.com.

    Regards,
    Ino Kiourtsidou

    KIOUR

  13. #13
    Join Date
    Jun 2005
    Location
    england
    Age
    68
    Posts
    25
    Rep Power
    0

    Re: Kiour controller problem ?

    I would buy an Eliwell ID961 a probe and 12v tranny and fit these.
    Full program in box easy to install, off cycle programable defrost, works fine on these units MPS same as Blizzard from Pentlands

  14. #14
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Kiour controller problem ?

    gday tony
    im in preference to 240 volt controllers being cheaper and easier to install.dixell comes to mind and have similar parameter descriptions to elliwell.cheers
    mmm to beer or not to beer...........lets drink breakfast

  15. #15
    aussie fridgy's Avatar
    aussie fridgy Guest

    Re: Kiour controller problem ?

    Quote Originally Posted by lowcool View Post
    gday tony
    im in preference to 240 volt controllers being cheaper and easier to install.dixell comes to mind and have similar parameter descriptions to elliwell.cheers
    which dixell??? to replace the kiour ref-df-sm>>>>

  16. #16
    Benschop1's Avatar
    Benschop1 Guest

    Re: Kiour controller problem ?

    Common problem with the kiour controller. Google MPS Wholesale and order same controller from Mark. Quite expensive, but will normally come pre programmed with all parameters. Many universal controllers will do the triack but if yours has the water level sensor for the evaporative tray and a fan door switch, this is the easiest solution.

    T

  17. #17
    Benschop1's Avatar
    Benschop1 Guest

    Re: Kiour controller problem ?

    If you want a 240v controller try the Elae AT2 about £30.00 from Hawco refrigeration.

Similar Threads

  1. serve over problem
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 17-06-2009, 03:28 AM
  2. Honeywell tuscan 5 controller problem
    By dunny123 in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 24-03-2009, 09:11 PM
  3. YORK YCAM Controller problem
    By Ockert in forum Trouble Shooting
    Replies: 2
    Last Post: 21-02-2009, 12:01 PM
  4. mitsubishi vrf problem!
    By airconadam in forum Air Conditioning
    Replies: 16
    Last Post: 08-11-2008, 06:50 PM
  5. Kiour Controller
    By nemesis740 in forum Commercial
    Replies: 5
    Last Post: 01-06-2008, 10:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •