Results 1 to 17 of 17
    May 2009
    texas
    7
    high suction pressure
    ive been working on a goodman a/c thats about 6 yrs old suction pressure is 200 head pressure is 200. did a amp check on the compressor it 23. rla is 12.1 . the amps seemed high is this normal? evaporator is a little dirty but not bad. inside fan is blowing good. thanks for any info
    Auckland
    74
    3,357
    38
    Re: high suction pressure
    It would appear that the compressor has stalled and drawing lock rotor amps.
    Split Croatia
    57
    6,151
    36
    I would expect lock rotor amps to be 5-7 times of full load amps (rla).
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by david ashley View Post
    Is that heat pump or only cooling A/C?
    May 2009
    texas
    7
    no, this is not a heat pump.
    Aug 2007
    Perth, West Australia
    55
    11
    Let me get this straight. The compressor is running and the suction and head pressure are the same? If this were a hermetic with this problem, I would say that the discharge line inside the compressor has broken and the refrigerant is recirculating inside it. If this is the case, suction line entering will be warmer than expected and discharge line leaving will be cooler than expected.
    Jan 2008
    India
    70
    171
    Suction Pressure and discharge pressure both are 200 PSI seems that the system might have been recently topped up with refrigerant and it appears overcharged as both suction and discharge are same.
    Please remove refrigerant till suction is around 60 to 70 PSI for R-22 and check.
    Dec 2008
    UAE
    42
    171
    There are following possibilities
    1. Relay is functioning wrong
    2. The run and start winding getting short, check for Resistance of both
    3.the discharge line inside the compressor has broken and the refrigerant is recirculating inside it and for verification you can check the discharge will be colder than compressor dome temperature.
    4.You can also check for noise (abnormal) from the compressor.
    Amit Saxena
    Jul 2009
    Berkshire
    175
    15
    Should be (not always) a contactor overload to prevent sustained high current draw. Or the MCB or fuses supplying the unit may be way over the required rating. This should be checked too otherwise serious compressor damage or even fire could be caused.
    Feb 2008
    adelaide sth.oz
    1,015
    ill go a carton that the start capacitor is open circuit,dont reckon locked rotor amps are high enough,and op has hearing problems,broken pipe would be under amp i reckon saturated.
    cheers fellas
    Last edited by lowcool; 09-08-2009 at 01:12 PM. Reason: had belt drive single phase to this current havent done a tin can but
    Aug 2008
    Baltics
    786
    Of course with broken compressor valve(s) current drawn is much less than the rated one.
    Apr 2001
    79
    5,071
    35
    Are we assuming the compressor is a recip? Maybe it is a scroll.
    Mar 2006
    belfast
    239
    what are the standing pressures and what happens to these when the comp gets power?
    can you pump test the comp?
    May 2009
    texas
    7
    thank you all for the help
    Auckland
    74
    3,357
    38
    Low Cool.
    You are a cool guy, 99% of posts would not even remotely understand your post. But I do and your on the button.,
    Feb 2008
    adelaide sth.oz
    1,015
    what you been on magoo?
    less time speakin,more time for drinkin!
    did have a chuckle over garys post didnt think of that one,i might see a goodman compressor one day
    Aug 2009
    Turhona.libya
    79
    15
    There are only 2 cases which we could get the said pressure's reading. It's ether compressor's valves are broken or a broken discharge line inside the compress's dome. which mean the compressor is pumping the refrigerant to the suction line directly ,this case will increases the drawn amps where the broken valve decreases the drawn amps
  1. need help! compressor kicking out on high pressure
    By SloFuse in forum Trouble Shooting
    Last Post: 19-08-2009, 04:46 PM
  2. Pressure drop through the suction line accumulator?
    By frank721 in forum Technical Discussions
    Last Post: 14-07-2009, 06:06 AM
  3. High Suction Temps
    By freezerman11 in forum Trouble Shooting
    Last Post: 30-06-2009, 08:11 PM
  4. Benji