Beer cooler : have I charged it correctly?
Like a lot of other engineers, I was taught that a full site glass means the unit is charged correctly. I have learnt so much on this forum in the last two weeks about superheat and subcooling and doing it scientifically rather than by feel. So I would like to explain a job I did today on a callout and give you all the figures I measured, and then leave it to the experienced boys to comment on it. CONSTRUCTIVE CRITICISM ONLY PLEASE!!
An NRS Beer Master that runs on R134a had lost its charge due to a capillary wearing through against the discharge pipe. Cut a long story short, replaced the LP switch, put in a new drier, pressure tested to 200 PSI (@55'C SLT), evacuated to 4 Torr and started charging it. The evaporator uses an internally equalised TEV. Condenser fan runs at 1 speed. Cellar setpoint 13'C.
Initially I put in 2 KG and watched the site glass as it started to fill up. Before it was completely full, I stopped and allowed the system to run for 10 minutes to stabilize.
Readings: 20 degrees on condenser
31 degrees off condenser
23'C on evaporator
13'C off evaporator
36 PSI suction pressure
14'C SST
115 PSI liquid pressure
33.5'C SLT
So that gives me 9K superheat and 1.5K subcooling. My understanding of that is that it is still short of refrigerant. I also realise that we should only really be taking these measurements when room is close to design temperature. This will take hours to get there due to all the warm beer kegs though.
I continued to add small quantities of refrigerant in 50g intervals and monitored SH and SC values, which did not change much.
I then blocked up the condenser coil to simulate warmer days and pushed the values up as follows:
20 degrees on condenser
41 degrees off condenser
19'C on evaporator
11'C off evaporator
40 PSI suction pressure
16'C SST
160 PSI liquid pressure
45'C SLT
Obviously the unit has been running for awhile, so the room temperature is dropping slowly.
So now my SH is 9K and my SC is 1.5K. No change????
I have stopped charging at 2.5KG and the best SC I got was 2K and the SH stays at 9K. The cellar temp down to 18'C and off evaporator at 11'C.
So the big question, was I on the right track? My concern is that if I keep charging it while the room is still about 5 to 7'C from design temperature, that I am making a mistake. I was aiming for a SC value of between 4.5K and 8.5K. The SH would be 60%-70% of the evaporator TD.
Thanks in advance for your answers!
-
07-08-2009, 10:40 PM #2
Re: Beer cooler : have I charged it correctly?
First let's start with abbreviations and definitions:
SST = Saturated Suction Temp
SLT = Suction line temp
SCT = Saturated Condensing Temp
LLT = Liquid Line Temp
TD is the difference between air on temp and saturation temp.
dT is the difference between air on temp and air off temp.Last edited by Gary; 07-08-2009 at 10:47 PM.
-
07-08-2009, 11:09 PM #3
Re: Beer cooler : have I charged it correctly?
20 degrees on condenser
31 degrees off condenser
Cond dT = 31-20= 11K dT
23'C on evaporator
13'C off evaporator
Evap dT = 23-13 = 10K dT
36 PSI suction pressure = 5C SST
TD = 23-5 = 18K TD
14'C SLT
Expected SH = 18*.6 to 18*7 = 10.8K to 12.6K
SH = 14-5 = 9K SH
115 PSI liquid pressure = 35C SCT
33.5'C LLT
35-33.5 = 1.5 SC
High SH + Low SC = System undercharged.Last edited by Gary; 07-08-2009 at 11:47 PM.
-
07-08-2009, 11:42 PM #4
Re: Beer cooler : have I charged it correctly?
20 degrees on condenser
41 degrees off condenser
Cond dT = 41-20= 21K dT
19'C on evaporator
11'C off evaporator
Evap dT = 19-11 = 8K dT
40 PSI suction pressure = 7C SST
TD = 19-7 = 12K TD
16'C SLT
Expected SH = 12*.6 to 12*.7 = 7.2K to 8.4K
SH = 16-7 = 9K SH
160 PSI liquid pressure = 46C SCT
45'C LLT
46-45 = 1K SC
21K cond dT = Insufficient cond airflow
High SH + Low SC = System undercharged.Last edited by Gary; 08-08-2009 at 01:34 AM.
-
07-08-2009, 11:51 PM #5
Re: Beer cooler : have I charged it correctly?
Unblock the condenser (blocking it was not necessary) and add more refrigerant.
Last edited by Gary; 08-08-2009 at 01:45 AM.
-
08-08-2009, 12:55 AM #6
Re: Beer cooler : have I charged it correctly?
The TEV could be an MOP , restricting load on compressor at high space temperature.
-
08-08-2009, 02:14 AM #7
Re: Beer cooler : have I charged it correctly?
-
08-08-2009, 03:24 AM #8
Re: Beer cooler : have I charged it correctly?
Hi Gary.
I have been confused by similar problems in the past, system drops into line approaching design. The TEV MOP vavs are a good idea so long as you know they are installed.
magoo
-
08-08-2009, 03:27 AM #9
Re: Beer cooler : have I charged it correctly?
@Magoo:
How would you be able to check whether the TEV was MOP, in the field?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
08-08-2009, 03:47 AM #10
Re: Beer cooler : have I charged it correctly?
MOP or not, the TXV cannot control the flow of liquid if there is no liquid to control.
The SC is much too low for the TXV to function properly.
-
08-08-2009, 03:49 AM #11
Re: Beer cooler : have I charged it correctly?
Hi desA.
Normally indicated on power head with Danfoss, others are by model number. Very confusing I know.
From memory ,danfoss low temp are -10C medium temp + 10C. Travel with all supplier catalogues is best advise. Danfoss, sporlan, Flicker, alco. And all and sundry.
magoo
-
08-08-2009, 03:55 AM #12
Re: Beer cooler : have I charged it correctly?
Hi Gary.
Way back on original post, there was a clear sight glass, ie., full flow available to TEV, correct me if I am wrong.
-
08-08-2009, 04:13 AM #13
Re: Beer cooler : have I charged it correctly?
If the sightglass is clear, then his subcooling measurements are wrong.
Hmmmm... in particular the liquid line temps are suspiciously high... way above cond air on temps.Last edited by Gary; 08-08-2009 at 04:33 AM.
-
08-08-2009, 04:42 AM #14
Re: Beer cooler : have I charged it correctly?
Hi Gary.
I would suggest that the system is undersized, and that the MOP vav is half protecting compressor under high duty loadings.
The up-side of MOP vavs is if undersized system at high duty then the heat of compression is taxing the condenser, hence minimal sub-cooling of liquid,but keeping compressor within limits.
-
08-08-2009, 04:56 AM #15
Re: Beer cooler : have I charged it correctly?
I wonder if the OP could explain a bit more about how the condenser exit temps were taken?
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
08-08-2009, 05:01 AM #16
Re: Beer cooler : have I charged it correctly?
Let's take a wild guess and say he is measuring the condenser outlet instead of the receiver outlet.
And possibly this unit has the receiver under the condenser?
-
08-08-2009, 05:12 AM #17
Re: Beer cooler : have I charged it correctly?
An undermount receiver would explain it. The condenser dumps straight down into the receiver with no liquid seal and no subcooling between the condenser and receiver. If he measured the temp at the condenser outlet, there would be little if any subcooling.
Last edited by Gary; 08-08-2009 at 05:34 AM.
-
08-08-2009, 07:51 AM #18
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
08-08-2009, 08:59 AM #19
-
08-08-2009, 09:04 AM #20
Re: Beer cooler : have I charged it correctly?
The condensing unit is supplied with shut off service valves, identical to a split system. The LLT was taken at the point the gauges are attached on the service valve. The SH measurement was taken from the suction gauge on the return service valve and the SLT at the evaporator where the bulb is mounted. Thanks desA.
-
08-08-2009, 09:07 AM #21
-
08-08-2009, 09:15 AM #22
Re: Beer cooler : have I charged it correctly?
The receiver is at the same level as the condenser. It's a small upright receiver. Don't quote me on this, but now that I remember, the condenser puts liquid in at the bottom and the liquid is drawn out the top and then through a drier, site glass etc. Thanks for your comments Gary. I will get my abbreviations right in future!
-
08-08-2009, 09:26 AM #23
-
08-08-2009, 09:30 AM #24
Re: Beer cooler : have I charged it correctly?
It needs to be added here that the cellar is a normal room with a cement floor, not an insulated cold room. It had been high in temp for at least 24 hours. It contains approx. 20 beer kegs, all warm, so I am of the opinion it will take some time to get down to temp? As we all know, a fridge system will be capable of operating with a leak up to a point, where the indoor temps will slowly start to rise .... and then suddenly no cooling.
-
08-08-2009, 09:33 AM #25
Re: Beer cooler : have I charged it correctly?
You've got me wondering Gary. They have never maintained this unit and it was in a right state. Condenser blocked, evaporator half blocked. I blew the coils out from the other side with nitrogen and then did a chemical coil clean on the condenser coils, and then rinsed it out. With a 10 to 20 degree delta-T, maybe it's not clean enough?
-
08-08-2009, 10:55 AM #26
Re: Beer cooler : have I charged it correctly?
I've been thinking about this, and may change my mind on what I said earlier. (Should have looked harder at the fridge circuit ) I think the liquid receiver has only one access point in the top, where the liquid line is tee'd into it. It's a pump down system, so maybe they only use it as a storage vessel on off-cycle. It would give symptoms then of no liquid seal?
-
08-08-2009, 02:34 PM #27
Re: Beer cooler : have I charged it correctly?
Was the sightglass full?
Was the LLT measured near the sightglass?
-
08-08-2009, 02:46 PM #28
Re: Beer cooler : have I charged it correctly?
In another thread, Magoo presented the theory that during the pulldown the SH should be 60-70% of the TD.
I haven't tested this, but it makes very good sense. The TD is an indicator of heat load and as the heat load decreases the TXV should close proportionately, resulting in proportionate SH.
For some reason the SH in this system is staying fixed at 9K as the TD drops, and we are wondering if this might be as a result of a MOP charge in the TXV bulb.Last edited by Gary; 08-08-2009 at 02:51 PM.
-
08-08-2009, 02:59 PM #29
Re: Beer cooler : have I charged it correctly?
-
08-08-2009, 03:51 PM #30
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Beer cooler : have I charged it correctly?
Last edited by nike123; 08-08-2009 at 03:55 PM.
-
08-08-2009, 03:53 PM #31
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
08-08-2009, 04:34 PM #32
Re: Beer cooler : have I charged it correctly?
At very low ambient temps the airflow should be blocked off to simulate warmer ambient, but one would think that the system would already have a fan control for that purpose.
Subcooling is limited by ambient temp. For example, if the SCT is 60F/15.5C and the ambient is 50F/10C, then it is not possible to achieve 15F/8.5K SC, because the TD is only 10F/5.5K.
I'm thinking a proportionate rule could be devised for SC, similar to Magoo's SH rule, i.e. SC = 60-70% of cond TD. This should be tested to get the right proportions.
-
08-08-2009, 10:46 PM #33
Re: Beer cooler : have I charged it correctly?
Have a read of this Sporlan document about TEVs, an explanation of MOP starts on page 6.
http://sporlan.jandrewschoen.com/10-9.htm
Also click on the Literature section, there is a lot of useful information there.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
09-08-2009, 01:08 AM #34
Re: Beer cooler : have I charged it correctly?
Acnerd
MOP stands for maximum operating pressure, TEV limits liquid feed rate. Check Brian_UK's connect to Sporlan
-
09-08-2009, 09:21 AM #35
-
09-08-2009, 09:36 AM #36
Re: Beer cooler : have I charged it correctly?
Thanks, interesting reading. They say MOP TEV's are generally used in a/c applications to prevent compressor loadings in high demand times where the evaporator is warm and the TEV would be open wide. Obviously I would have to check the beer cooler again, but in my understanding of what the MOP TEV does, it would be wasted on this system? It would have a 2 degree dead band, run between say 12 to 14'C and the difference in evaporator pressure between on and off cycle would only be a few PSI? At design temperature, the TEV wouldn't be opening to maximum, would it?
-
09-08-2009, 04:30 PM #37
Re: Beer cooler : have I charged it correctly?
I don't see how it would be possible to have a clear sightglass with only 1-2K SC. And the liquid line temp measurement is way above ambient.
I'm thinking your temp measurement is way off. What type of instrument are you using to measure the temps? Has it been calibrated?Last edited by Gary; 09-08-2009 at 04:33 PM.
-
10-08-2009, 04:37 PM #38
Re: Beer cooler : have I charged it correctly?
Ok, went to the van and got it out. It's a digital thermometer using K-type thermocouples. I make use of a surface touch probe which is about 3 months old. The thermometer was calibrated in Jan 2009.
This is a link for it..... if it works.
http://uk.rs-online.com/web/search/s...6-3738&x=0&y=0
I am going back tomorrow to carry out final adjustments on the LP switch now the room is down to setpoint temperature. I will take the measurements again and report back.
No-one has answered my question yet : can I get accurate SC and SH measurements when the room is not at design temperature?????? With a lot of heat to remove, would the SH not be higher than normal, and the SC lower than normal???
-
10-08-2009, 05:00 PM #39
Re: Beer cooler : have I charged it correctly?
-
10-08-2009, 05:19 PM #40
Re: Beer cooler : have I charged it correctly?
Peter_1 put the following statement to me another thread:
"Therefore I show students the measuring fault of their meters. They know the evaporating temperature of the system. They have to measure on several bends (the first ones) of an evaporator. They never measure evaporating temperature but some degrees higher (+/-3 to 5°C higher) This is partially due to the thermal resistance of the copper. This is then their measuring fault and this value can also be used at the outlet of the evaporator when measuring SH."
I never knew I had to make allowances for the material I was measuring? Is that where I am going wrong then?
-
10-08-2009, 05:27 PM #41
Re: Beer cooler : have I charged it correctly?
-
10-08-2009, 05:32 PM #42
Re: Beer cooler : have I charged it correctly?
Thanks for your help Gary, I'll post the final measured values tomorrow night when I get home.
-
11-08-2009, 04:25 PM #43
Re: Beer cooler : have I charged it correctly?
Ok here are the final measurements:
Room setpoint: 13'C
Evaporator air on: 14'C
Evaporator air off: 9.5'C
Suction pressure: 30 PSI
SLT: 8'C to 12.5'C (TEV hunting?)
Condenser air on: 22.5'C
Condenser air off: 33.5'C
Liquid pressure: 110 PSI
LLT: 33'C to 35'C (why???)
So the SH varies between 4K and 8.5K and the SC between 1K and -1K.
Sight glass full during operation!
If you work out the evaporator TD based on the above figures, then the SH should be between 1K and 4K ..... a bit low?
So something is not right in the design of this system. True or False?
-
11-08-2009, 04:34 PM #44
Re: Beer cooler : have I charged it correctly?
-
11-08-2009, 04:37 PM #45
Re: Beer cooler : have I charged it correctly?
Something is very wrong with the SC measurements. Negative SC is not possible. Either the LLT measurement is wrong or the high side gauge measurement is wrong.
-
11-08-2009, 04:41 PM #46
Re: Beer cooler : have I charged it correctly?
Attach your high side gauge to a container of refrigerant and a temperature probe to the side of the container. The temperature should correspond to the pressure on a P/T chart. If they do not correspond then either the gauge is out of calibration or the temp probe is out of calibration.
Last edited by Gary; 11-08-2009 at 04:45 PM.
-
11-08-2009, 04:43 PM #47
Re: Beer cooler : have I charged it correctly?
At this point, I am thinking that the gauge reading must be off (although it could still be the temp probe) and the system overcharged. Overcharge can cause the SH to hunt.
-
11-08-2009, 05:02 PM #48
Re: Beer cooler : have I charged it correctly?
OK, here's what I found:
R134a: Hp and LP both measure 70 PSI, bottle is 22'C
P/T chart shows: approx 74 PSI at 22'C
R22: Hp and Lp both measure 120 PSI, bottle is 22'C
P/T chart shows: 124 PSI at 22'C
I read in a fridge magazine that most engineers don't have their gauges adjusted to suit atmospheric pressure and it can throw SH and SC values out by a few degrees Kelvin. I have no idea if my gauges are perfectly correct or what the allowable error is. But as it stands, the gauge manifold is reading 4 PSI low or the temp probe is reading nearly 1 degree high!
-
11-08-2009, 05:38 PM #49
Re: Beer cooler : have I charged it correctly?
You might try putting your temp probe in icewater (stir the ice) to see if it shows 0'C.
-
11-08-2009, 05:42 PM #50
Similar Threads
-
Maxi 310 Beer Cooler
By Rabmax in forum CommercialReplies: 3Last Post: 20-08-2009, 04:45 PM -
R404A Beer Cooler
By NwBurbs in forum Trouble ShootingReplies: 5Last Post: 13-05-2009, 06:40 PM -
If Operating Systems Were Beers
By nike123 in forum Chit Chat & Service StoriesReplies: 1Last Post: 28-04-2008, 10:53 PM -
Saline solution in beer cooler
By Rabmax in forum Technical SpeculationsReplies: 2Last Post: 06-06-2007, 06:58 PM -
Cervitor Kitchens Beer Keg Cooler
By doogdoog in forum FundamentalsReplies: 5Last Post: 16-10-2006, 09:48 PM