Thread: Big Frick was locked up
-
06-08-2009, 09:34 PM #1
Big Frick was locked up
Hi
I have a question. We obtained a new/damaged Frick 88something bare screw that was locked up tight
After disassembly we found that it had water in the disc end rusting the inside and reducing the last 2 inches of rotor lip seals to nearly nothing.
From my old days I know could rework that lip seals, but what happens if we just clean it up and not repair that last section of rotor. The housing has some pitting, but can we just hone it down and expect ok operation
Your comments and suggestions are appreciated.
Oh yes I was with frick years ago been with Trane a few yrs and now with GEA and their Polacel cooling towers Need a tower let me know...
I wil attach a pic when i get it to load..
Bruce
-
07-08-2009, 02:39 AM #2
Re: Big Frick was locked up
I've reassembled machines that had the lip seals ground off and only had minimal capacity loss. New Mycom screws don't have lip seals on the edge of the rotor. I would just take the roughness off the housing but wouldn't try to remove the pits completely if it meant removing too much metal. I'd be more concerned about the surfaces in the clearance space between rotor and outlet housing.
-
07-08-2009, 02:49 AM #3
Re: Big Frick was locked up
Lip seal clearances give compressor efficiency, loose that clearance will reduce flow rate and create high by-pass and high oil/discharge temps., pitting in barrel will add to in-efficiency. best advise is scrap it. You could increase oil flow rate to compensate, but will be really growly.
The last time I looked Mycoms had the same rotor lip seals.
magoo
-
07-08-2009, 08:31 AM #4
Re: Big Frick was locked up
Pictures will help , but i'd agree with
CanadianIce .
I have pulled plenty apart with major damage and no one new about problem until then .
Its sometimes up to someones budget as well .
-
07-08-2009, 04:24 PM #5
Re: Big Frick was locked up
I would like to see some pictures...
-
07-08-2009, 08:40 PM #6
Re: Big Frick was locked up
Here are two pics I have Hope you can see them ok
-
07-08-2009, 10:55 PM #7
Re: Big Frick was locked up
Bruceboldy ,
Its a lot different than you originally described as its had a meltdown .
You still could overhaul it if you were desperate also depending on rotor casing damage we havn't seen . But it wouln't be worth the trouble or expense .
Get a new one
-
07-08-2009, 11:31 PM #8
-
08-08-2009, 03:45 PM #9
Re: Big Frick was locked up
He Bruceboldy,
all depends on what your customer wants. If they don't care and just want something that does 80% of what it supposed to do then after some grinding and polishing you could create a compressor that will work, but if you want to perform a refrigeration engineer worthy overhaul this rotorpair is finished. Indeed it looks like the rotors have seized quite a bit. You want to give your customer some guarantee that the compressor will operate the full 40 or 50.000 hrs. that it normally should do. If you are going to overhaul the compressor with these rotors at least have it checked for unbalance or else all your effort is for nothing when the compressor is started up and somebody wants to do a vibration analyses on the compressor.
The Screwdoctor
Similar Threads
-
Frick screw compressor SGC3515 overhaul manual
By cjlee74 in forum IndustrialReplies: 10Last Post: 13-10-2010, 08:49 AM -
problem with volume on frick screw compressor
By samlee12 in forum IndustrialReplies: 4Last Post: 29-10-2009, 06:06 AM -
problem with frick screw volume
By samlee12 in forum Industrial CompressorsReplies: 9Last Post: 20-06-2009, 02:46 PM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM -
Compressor Check for locked rotor voltage
By shogun7 in forum Trouble ShootingReplies: 0Last Post: 04-04-2004, 12:44 AM