    McQuay ALS F XE273.2 990Kw, highest return temp?



    Hi Gents

    Anyone know the McQuay maximum return water temp for these chillers? McQuay ALS F XE273.2. 990Kw cooling capacity.

    I have increased plant supply water to 14*C with a return of 17*C. I have been told it can handel 20*C return water because of compressor liquid injection. Is this correct or am i getting duff info?
    Talking to Mcquay tech line is like pulling teeth and getting conflicting stories.

    I have converted a data centre to supply air control and have saved 20% on chiller loading, plant water has increased 4K to double the free cooling operational time. I will publish my findings later on.

    Cheers guys

    Wombat



  2. #2
    Join Date
    Feb 2009
    Location
    UK
    Posts
    36
    Rep Power
    0

    Re: McQuay ALS F XE273.2 990Kw, highest return temp?

    here's a chart of my savings
    Attached Images Attached Images

Similar Threads

  1. Best place for return air sensors, in the room or ceiling void?
    By back2space in forum Air Conditioning
    Replies: 27
    Last Post: 06-07-2009, 06:21 AM
  2. how to determine air return temperature
    By firmanardha in forum Air Conditioning
    Replies: 6
    Last Post: 31-01-2009, 03:34 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •