    Flooded water chiller with hot gas supply for agitation



    Does anybody have experience to work with flooded water chillers which use hot gas for ammonia agitation?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Flooded water chiller with hot gas supply for agitation

    Do you mean like a majonier with injector ?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded water chiller with hot gas supply for agitation

    I have used hot gas bypass on chillers to prevent freeze-up or operation at very low loads, but agitation? What are you trying to accomplish Segei?
    If all else fails, ask for help.


  4. #4
    Join Date
    Jul 2009
    Location
    New zealand
    Age
    47
    Posts
    15
    Rep Power
    0

    Re: Flooded water chiller with hot gas supply for agitation

    Thats cool hot gas agitation?

  5. #5
    Join Date
    Jul 2009
    Location
    New zealand
    Age
    47
    Posts
    15
    Rep Power
    0

    Re: Flooded water chiller with hot gas supply for agitation

    whats going to happen with dicharge pressure of those compressors?

  6. #6
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Flooded water chiller with hot gas supply for agitation

    I heard that this hot gas use to improve heat transfer and manufacturer require certain minimum hot gas pressure. It can be barrier to lower condensing pressure. I believe that boiling ammonia has very good heat transfer coefficient and it doesn't require agitation. So I'm puzzled as well.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded water chiller with hot gas supply for agitation

    Well... the only thing I can think of right now is someone is trying to convince themselves that injecting hot gas into the liquid in a flooded chiller will promote nucleate boiling instead of pool boiling. This might be an attempt to improve load load performance???

    The downside is that even though the hot gas will be cooled down to the saturation temperature in the chiller the extra gas still has to be compressed and that costs energy.
    If all else fails, ask for help.


Similar Threads

  1. York Chiller evap water flow direction
    By mechillers in forum Technical Discussions
    Replies: 6
    Last Post: 30-03-2009, 05:37 PM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  4. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •