    water cooled condenser



    hi,

    symtoms are

    high head pressure @ 23 brg.
    discharge temp @ 85c
    suction pressure @ 10brg
    suction temp high @ 20c
    high compressor amps @ 9 ish amps x 3

    it is a trane dx water cooled condenser, with a head pressure regulator...checked temps across reg and it is fully open to the condenser bundle, anybody got tips on good confirmation that the hex is insufficent??..overcharged has crossed my mind but discharge temp is higher than normal

    rgds phil



  2. #2
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: water cooled condenser

    Hello
    What are the water temp's

    FIXIT

  3. #3
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: water cooled condenser

    Sounds like shed loads of non-condensibles to me.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    hi,

    symtoms are

    high head pressure @ 23 brg.
    discharge temp @ 85c
    suction pressure @ 10brg
    suction temp high @ 20c
    high compressor amps @ 9 ish amps x 3

    it is a trane dx water cooled condenser, with a head pressure regulator...checked temps across reg and it is fully open to the condenser bundle, anybody got tips on good confirmation that the hex is insufficent??..overcharged has crossed my mind but discharge temp is higher than normal

    rgds phil

    Pressure doesn't mean anything without knowing what refrigerant is. If that is R410A then pressures "looks good".

    Also without evaporator air in and out temperatures and condenser water in and out temperatures, nothing meaningful can be said about system problem.
    What is "hex"?

    What means "high compressor amps @ 9 ish amps x 3"?

    Please without slang. We are not gang members, we are refrigeration engineers and we need precise language for understanding descriptions of our problems.

  5. #5
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    ok
    high load in the room...air on 31c and 26c off with 2 stages of cooling running....

    the system operates on r407c
    the other stages superheats, subcooling,discharge temp is ok and has a running amps of 7.6 ,7.8 ,7.2...
    i am getting a differences of 3 degrees between condenser water in and out on both bundles..

    aswell back pressure is 5 brg but superheat is 18c..
    subcooling is also low 5c

    any more info?
    Last edited by philjd26; 05-08-2009 at 09:29 PM.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    ok
    high load in the room...air on 31c and 26c off with 2 stages of cooling running....

    the system operates on r407c
    the other stages superheats, subcooling,discharge temp is ok and has a running amps of 7.6 ,7.8 ,7.2...
    i am getting a differences of 3 degrees between condenser water in and out on both bundles..

    aswell back pressure is 5 brg but superheat is 18c..
    subcooling is also low 5c

    any more info?
    With a high load in the room, superheat will be high.
    Superheat can only be measured and set when the system is near or at design conditions.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: water cooled condenser

    Quote Originally Posted by HallsEngineer View Post
    Sounds like shed loads of non-condensibles to me.
    Yep... sounds like lots of air in the system.

    If we knew the water in/out temps that would confirm it.
    Last edited by Gary; 05-08-2009 at 10:17 PM.

  8. #8
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    temp on condenser inlet was 65 and 45 out...

    will reclaim and recharge tomorrow

    thanks men

    rgrds phil

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    temp on condenser inlet was 65 and 45 out...
    Are you saying the water entering the condenser is 65C?... or is that the water pressures?... or none of the above?
    Last edited by Gary; 05-08-2009 at 10:53 PM.

  10. #10
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    no, sorry water entering is 28c and 32c out of condenser..
    discharge gas entering 65 and 45 out of condenser...

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    no, sorry water entering is 28c and 32c out of condenser..
    discharge gas entering 65 and 45 out of condenser...
    The heat is not transferring from the very hot refrigerant to the very cold water. Either the water is bypassing in the end bell of the condenser (less likely) or the condenser is full of air (more likely).

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: water cooled condenser

    Do you have suction accumulator in your system? With R407C it should be without suction accumulator because of fractionation.
    http://www.refrigeration-engineer.co...37&postcount=3

  13. #13
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    thanks for reply gary.

    the condenser bundle is part of a bigger system consisting of many other condenser cooled by a main plant. also the condensers are located in a lower area to dry cooler, would this air not make its way to the top???

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    thanks for reply gary.

    the condenser bundle is part of a bigger system consisting of many other condenser cooled by a main plant. also the condensers are located in a lower area to dry cooler, would this air not make its way to the top???
    It is the refrigerant side of the condenser that is full of air, not the water side.

  15. #15
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    Quote Originally Posted by Gary View Post
    It is the refrigerant side of the condenser that is full of air, not the water side.
    ok thanks again..

  16. #16
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: water cooled condenser

    hi
    still have no solved this problem ...however i have further information...

    this curcuit has a head pressure regulator, could this be faulty and causing abnormal head pressure/temp and suction head/temp....

    the unit is a trane CCU model no. EUEB2208A

    any sure test to confirm the regulator??

    rgrds phil

  17. #17
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: water cooled condenser

    Quote Originally Posted by philjd26 View Post
    hi,

    symtoms are

    high head pressure @ 23 brg.
    discharge temp @ 85c
    suction pressure @ 10brg
    suction temp high @ 20c
    high compressor amps @ 9 ish amps x 3

    it is a trane dx water cooled condenser, with a head pressure regulator...checked temps across reg and it is fully open to the condenser bundle, anybody got tips on good confirmation that the hex is insufficent??..overcharged has crossed my mind but discharge temp is higher than normal

    rgds phil
    For r407c, at LP of 10barg=11.01bar(a)
    Te,sat=28.2'C (Coolpack)

    Something does not stack up with your numbers...

    If your LP is fairly high, then I'd imagine your system is over-charged with refrigerant... grossly overcharged.
    Last edited by desA; 18-11-2009 at 02:48 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. R410A water cooled condenser
    By K.R.Iyer in forum Fundamentals
    Replies: 0
    Last Post: 04-02-2009, 02:10 AM
  2. water cooled condenser
    By langy in forum Air Conditioning
    Replies: 2
    Last Post: 19-08-2008, 06:43 PM
  3. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  4. How to adjust head on a water cooled condenser
    By kengineering in forum Technical Speculations
    Replies: 5
    Last Post: 30-05-2007, 10:37 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •