Oil draining port position?(HFC,HCFC)
Dear all,
This is an old question. BUt it is puzzling me now. I want to know the position of oil draining in the flooded evaporator.
R717 with mineral oil, the oil draining port set on the bottom; R22 with mineral oil , the ports set on the upper liquid level.'Cause the mineral oil and R22/R717 is immiscible.
But to R507 with miscible oil, R23 with miscible oil, where is the position to set in the flooded evaporater?I met this matter in the R507/R23 cascade system. High temperature stage condensing temp. is 40C, evaporate temp.is -25C. Low stage running condition is -20C(condensing)/-75C (evaporating).
kindly regards,
sagittarius
-
07-08-2009, 02:30 AM #2
Re: Oil draining port position?(HFC,HCFC)
From what I've seen, if the refrigerant and oil are miscible, then you would set your oil drains at operating level. We set lines at 3 different levels, all slightly overlapping vertically to allow for surging of liquid. These are piped back to the oil still.
-
08-08-2009, 07:12 AM #3
Re: Oil draining port position?(HFC,HCFC)
I'm confused about that. It's the reason I bring up the question.
Miscible oil will blend with refrigeration at any liquid level. Whether you set the oil drain ports at the operation level or the bottom of vessle,the oil can't be drained mainly. THis is my puzzle.
Similar Threads
-
extra expansion valve and dryer port
By CoolWell in forum FundamentalsReplies: 8Last Post: 07-10-2008, 03:10 AM -
Understanding Balance port TX valves
By Mobbsy in forum Technical DiscussionsReplies: 12Last Post: 23-07-2008, 04:32 AM -
Looking for a source for stainless side port distributor
By 128cyclist in forum Technical DiscussionsReplies: 1Last Post: 21-06-2007, 10:07 PM -
Oil in the TEV equilizer port
By herefishy in forum Technical DiscussionsReplies: 3Last Post: 26-04-2002, 02:33 PM -
Balanced port TEVs
By Prof Sporlan in forum FundamentalsReplies: 22Last Post: 25-02-2002, 03:43 PM