04-08-2009, 01:19 AM #1
refrigerant flow question
Hi guys, When compressors are off of cycle, does the refrigerant still flow from discharge line to suction line through the compressor itself?
-
04-08-2009, 01:45 AM #2
Re: refrigerant flow question
Not generally,
If a sudden pressure equalization happens at stop, would indicate a busted discharge valve , this will allow pressures to balance quickly.Can you indicate what type of system you are referring to.
magooLast edited by Magoo; 04-08-2009 at 01:46 AM. Reason: added
-
04-08-2009, 02:20 AM #3
-
04-08-2009, 02:35 AM #4
Re: refrigerant flow question
desA,
can you be more specific. Exception being a screw compressor
magooLast edited by Magoo; 04-08-2009 at 02:38 AM. Reason: added
-
05-08-2009, 07:28 AM #5
Re: refrigerant flow question
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
07-08-2009, 10:02 PM #6
Re: refrigerant flow question
Peter is right. In general, compressor valves are not like intake/exhaust valves in a combustion engine where certain cam positions will leave a valve open. In recip machines, the valves function as check valves when the pistons are not moving. Gas really can't go the wrong way unless something breaks.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Flow Rate through Fan Coil Unit
By deepu in forum Air ConditioningReplies: 4Last Post: 21-07-2009, 06:42 AM -
Refriferation cycle question
By ozmecheng in forum FundamentalsReplies: 32Last Post: 26-03-2008, 10:38 PM -
what else i have to measure or evaluate in a mixture refrigerant for to improve it?
By mebluna in forum RefrigerantsReplies: 11Last Post: 24-04-2007, 09:48 PM