    Question low temp refriger superheat



    Hi, I have a question on superheat for low temp walk in freezer. when using negetive numbers what is the proper way to calculate the compressor and evap superheat. Example: I have a suction pressure temp at evap of -18 and temp at bulb is -12 do I have a 6degree superheat? If compressor suction temp is -18 and I have a pipe temp of +10 would that be a 28 degree superheat. Example at compressor: -25 and -5 om pipe ? would that be 20 degree superheat?? Thanks for all replys Paul



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low temp refriger superheat

    Correct... correct... and correct.

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: low temp refriger superheat

    Correct, correct and correct . A part is useful superheat the rest is non useful superheat.
    To make progress is never good enough, I want to do better and better and better

  4. #4
    paulsref's Avatar
    paulsref Guest

    Re: low temp refriger superheat

    Thank you all for the confirmation!! I sometimes second guess myself and it is nice to get confirmation that I am on the right track. Thanks again Paul

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: low temp refriger superheat

    When temp measured at suction valve & tex outlet , it becomes total system superheat which has a bearing on discharge end temp of compressor . Neither high superheat nor total superheat is desireable

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: low temp refriger superheat

    Quote Originally Posted by D.D.KORANNE View Post
    Neither high superheat nor total superheat is desireable
    I don't agree totally with you.
    For R404A and R507 and other gases of this kind higher useful superheat is harmless (not exagerated superheat) - 20 K for instance - It is advantageous due to increased capacity and the discharge temperature are not very high.
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. Refrigeration 101
    By Gary in forum Fundamentals
    Replies: 201
    Last Post: 01-11-2011, 10:18 PM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  4. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •