    General Inverter AOH12LSAC



    Hi Everyone can anyone help, i was called to look at a General Inverter ( Fujitsu ) and found that the system would run for approx 3/4 mins before going into a fault mode and the red LED on the outdoor board flashed 22 times does anyone have any info on error codes or a manuel.

    The unit was installed in 2002

    Thanks



  2. #2
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: General Inverter AOH12LSAC

    Will try and find out next week for you, did you get the indoor unit error code display patterns?
    They have two levels of display on the indoor unit, you need note the first display then press the test run button on the remote (aim it at the unit of course!) and the flash pattern on the indoor unit will change showing the second part of the error code display.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: General Inverter AOH12LSAC

    Self diagnose.png

    .................


    After you perform self diagnosis inform us abut found error code.

  4. #4
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    16

    Re: General Inverter AOH12LSAC

    Thanks Nike123 will keep you informed, the client has gone back to England and cannot access his home until he is back.

  5. #5
    Join Date
    Jul 2008
    Location
    Australia
    Age
    76
    Posts
    21
    Rep Power
    0

    Re: General Inverter AOH12LSAC

    You need to count the number of times the light goer out not on. The closest I can come to is 21 offs which is abnormal voltage at active filter module. This is a DC device which amplifies the voltage to about 360 volts DC up to 380 volts DC. It refers to the output voltage so you need to test this, usually a yellow & a blue wire.

  6. #6
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    16

    Re: General Inverter AOH12LSAC

    Quote Originally Posted by ozairman View Post
    Will try and find out next week for you, did you get the indoor unit error code display patterns?
    They have two levels of display on the indoor unit, you need note the first display then press the test run button on the remote (aim it at the unit of course!) and the flash pattern on the indoor unit will change showing the second part of the error code display.
    Hi Ozairman sorry it has taken so long, client went back to the UK just to let you know that the first part of the error code is 8 flashes on the red lamp with the green one flashing constantly. The second part of the error code is the red lamp flashing constantly and the green lamp flashes 3 times.

    Any ideas

  7. #7
    Join Date
    Oct 2009
    Location
    UK
    Posts
    5
    Rep Power
    0

    Re: General Inverter AOH12LSAC

    We support inverter repairs,
    try ndc-uk.com

Similar Threads

  1. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  2. 600w inverter powerful enough??
    By polly in forum Trouble Shooting
    Replies: 4
    Last Post: 21-02-2010, 10:25 AM
  3. Daikin Inverter Board / Compressor issues
    By Greengrocer in forum Air Conditioning
    Replies: 12
    Last Post: 21-04-2009, 10:12 PM
  4. Difference between AC Inverter & DC Inverter Compressor
    By berrytmy in forum New Technologies
    Replies: 0
    Last Post: 24-04-2008, 11:43 AM
  5. Inverter systems
    By Latte in forum The Trail of Tears
    Replies: 23
    Last Post: 11-07-2007, 12:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •