Hi Everyone can anyone help, i was called to look at a General Inverter ( Fujitsu ) and found that the system would run for approx 3/4 mins before going into a fault mode and the red LED on the outdoor board flashed 22 times does anyone have any info on error codes or a manuel.
The unit was installed in 2002
Thanks
-
01-08-2009, 06:11 AM #2
Re: General Inverter AOH12LSAC
Will try and find out next week for you, did you get the indoor unit error code display patterns?
They have two levels of display on the indoor unit, you need note the first display then press the test run button on the remote (aim it at the unit of course!) and the flash pattern on the indoor unit will change showing the second part of the error code display.
-
02-08-2009, 04:47 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: General Inverter AOH12LSAC
Self diagnose.png
.................
After you perform self diagnosis inform us abut found error code.
-
04-08-2009, 06:22 AM #4
Re: General Inverter AOH12LSAC
Thanks Nike123 will keep you informed, the client has gone back to England and cannot access his home until he is back.
-
07-08-2009, 05:25 AM #5
Re: General Inverter AOH12LSAC
You need to count the number of times the light goer out not on. The closest I can come to is 21 offs which is abnormal voltage at active filter module. This is a DC device which amplifies the voltage to about 360 volts DC up to 380 volts DC. It refers to the output voltage so you need to test this, usually a yellow & a blue wire.
-
31-08-2009, 04:41 PM #6
Re: General Inverter AOH12LSAC
Hi Ozairman sorry it has taken so long, client went back to the UK just to let you know that the first part of the error code is 8 flashes on the red lamp with the green one flashing constantly. The second part of the error code is the red lamp flashing constantly and the green lamp flashes 3 times.
Any ideas
-
13-10-2009, 04:49 PM #7
Re: General Inverter AOH12LSAC
We support inverter repairs,
try ndc-uk.com
Similar Threads
-
Testing Inverters
By fridge doctor in forum Air ConditioningReplies: 38Last Post: 15-06-2011, 06:52 AM -
600w inverter powerful enough??
By polly in forum Trouble ShootingReplies: 4Last Post: 21-02-2010, 10:25 AM -
Daikin Inverter Board / Compressor issues
By Greengrocer in forum Air ConditioningReplies: 12Last Post: 21-04-2009, 10:12 PM -
Difference between AC Inverter & DC Inverter Compressor
By berrytmy in forum New TechnologiesReplies: 0Last Post: 24-04-2008, 11:43 AM -
Inverter systems
By Latte in forum The Trail of TearsReplies: 23Last Post: 11-07-2007, 12:14 AM