    R1270 system oil return question



    In R717 system,the R717 density is lower than oil,and they are not dissolve.SO we can separate the oil in condenser or receiver.But in R1270 system,I know R1270 density is lower than oil(is it right?).but I don't know if they are dissolve each other like R22,If they are dissolve each other,I think only the evaporator need a oil collector.I use CPI synthetical oil.



  2. #2
    Join Date
    Mar 2006
    Location
    China
    Posts
    86
    Rep Power
    18

    Re: R1270 system oil return question

    It is a different way to be solved.
    Normally the ammonia refrigeration systme use the mineral oil. On this condition the oil is weighter and exist on the bottom of flooded evaporator. I think it isn't necessary to consider the oil in condensor and high pressure receiver. If you use the miscible oil in the ammonia system (DX evaporator) ,don't care about that .
    R1270 refrigeration system use the CPI syn. oil. you can treat it same as ammonia. R1270 liquid density is smaller than oil.

Similar Threads

  1. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 04:18 PM
  2. Refrigeration system simulation and optimization
    By autt in forum System Optimization
    Replies: 7
    Last Post: 05-12-2008, 03:59 PM
  3. Cascade system question??
    By theapprentice in forum Fundamentals
    Replies: 8
    Last Post: 03-12-2008, 11:32 AM
  4. Automatic oil return system
    By matt watson in forum NH3
    Replies: 6
    Last Post: 29-03-2008, 07:24 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •