    Problem with mcquay chiller



    I have a mcquay chiller model
    SE LN MODEL MHG 091.2 with 2 compressor and i have this problem. On both circuits i have the same anomaly after few minute of work (high oil pressure diference). The circuit nr 2 have moments when is working fine for over 2 hours and after that the same error. Another thing what is bodering me is that the first compressor is no`t raising in capacity just staying in 12 %. I am no`t understending the error because i have only a transducer for oil and the error i belive is refering about a diferential presure swith for oil.Another thing is in the status for first circuit is (low dish sh).I must say i don`t have the papers for it . Please help. My best regard`s. Maybe some Pdf file if is possible for that carel display



  2. #2
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Problem with mcquay chiller

    The oil filter probably needs changing. If it says high diff oil pressure then yes oil filter requires changing. If low diff oil pressure then you need to throttle your suction till it gets going.

  3. #3
    MQFS Mo's Avatar
    MQFS Mo Guest

    Re: Problem with mcquay chiller

    I'm not familiar with the model number (they are different here in the States).
    A little more information about the unit would be helpful. Based on what you've said so far, I'd guess it is an Air cooled screw compressor?
    I have plenty of documents I can direct you to, but need to identify which US unit would be a closest match. (Even the USA made units were originally made in Italy, so they are essentially the same)

    It would most likely be a restrictes oil filter. They are supposed to be changed 500 hours or so after startup. Most don't, they simply monitor OPD & replace only if needed.

  4. #4
    Join Date
    Jul 2008
    Location
    GREECE
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Problem with mcquay chiller

    I THINK THE MODEL IS MNG . IF THE COMPRESSOR ARE WORKING FOR A LONG TIME AT MIN CAPACITY THEN THE OIL WILL OVERHEATING AND IT IS NORMAL TO FACE OIL DIFF ALARM . DO YOU CHECK DelicSupHeat ?

  5. #5
    Join Date
    Nov 2009
    Location
    Australia
    Age
    66
    Posts
    16
    Rep Power
    0

    Re: Problem with mcquay chiller

    Texanul,

    As Hallsengineer said, definatly change the oil filters, check the calibration of the transducers. 9 times out of 10 high oil diff. fault is the oil filter.

    Regards

    MQFS OZ

  6. #6
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    Re: Problem with mcquay chiller

    Hy texanul maybe can I halp u because I work with Mc Quay chiller ,if u e-mail me at baycuclaudyu@yahoo.com

  7. #7
    Join Date
    Nov 2008
    Location
    kent
    Posts
    25
    Rep Power
    0

    Re: Problem with mcquay chiller

    Hi texanul

    If its def an mng then running low lioad a long time will give u possibly a hagh discharge temp alarn breached at 110 c this can be solved with additional settings in a newer version off softwear or a shut down delta t setpoint adjustment, u wont have a oil pressure , diff arrangment but a comparison of oil and discharge pressures .

    WHY NOT MESSURE DISCHARGE AN OIL PRESSURES WITH A GAUGE MANIFOLD AN DO THE MATH ?
    If running at low load with low head mbe oil not i seperater but in condenser , mbe low load for long periods with rising dischargeb temp opens liquid injection and adds to low oil levels . although i'm told that this dont happen, if the other cuircuit runs at 25% is it evap pressure hold ?, wats your suctionpressure ?, wats your lvg chilled water set point and your freeze prevent and and how close to lvg set point are you ?


    The list goes on a bit to be honest ,,

    good luck

Similar Threads

  1. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  2. Chiller connectivity problem
    By ALLAHHOOPK in forum New Technologies
    Replies: 2
    Last Post: 12-05-2009, 05:57 PM
  3. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  4. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM
  5. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •