    Helium for leak detection

    I have just heard from a friend that Helium is used for detecting the smallest leaks in a system.
    The system evacuates and filled with Helium up to 15psi and the leak is detected with th regular electronic leak detector.

    Any comments?

    Chemi

  2. #2
    Join Date
    Jun 2002
    Location
    Surbiton, U.K.
    Posts
    47
    Rep Power
    0

    Re: Helium for leak detection

    Hi Chemi,
    Are you sure that it is an electronic leak detector and not an ultrasonic leak detector?
    "The old codger"

  3. #3
    Join Date
    Jul 2003
    Location
    Ireland
    Posts
    10
    Rep Power
    0

    Re: Helium for leak detection

    Helium was used more by manufacturers previously because the detector was hugely expensive, however I believe cheaper detectors have become available in the last few years.

    Helium doesn't detect smaller holes, however it does show leaks more quickly than standard leak tests, and that's why it was advantageous to manufacturers of coils who could process their production more cost effectively

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Helium for leak detection

    Hi donhoban.

    Isn't the molecule of Helium smaller, allow the gas to come out in smaller holes then refrigerants?

    Peter, I haven't a clue but ultrasonic detector is very uncommon with fridgy's.

    Chemi

  5. #5
    Join Date
    Jul 2003
    Location
    Ireland
    Posts
    10
    Rep Power
    0

    Re: Helium for leak detection

    Quote Originally Posted by chemi-cool
    Isn't the molecule of Helium smaller, allow the gas to come out in smaller holes then refrigerants?
    As I understand it, bearing in mind, I'm an engineer,not a phyisicist or chemist - molecular size of helium is about 10-10m or 0.0000000001 meters

    Say we assume the leak is 1/1000 of a mm across - we'd still potentially fit 1000 molecules of helium across the gap at any one time!

    So really, unless we start dealing with monster molecules, I don't think the relative size difference between helium and refrigerant is important.

    I could of course be wrong

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Helium for leak detection

    Hi donhoban.
    From what I've heard, this is why Helium is being used.

    I dont see any other reason.

    Chemi

  7. #7
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Helium for leak detection

    Helium has been used for many years in certain production methods where a high degree of system tightness is demanded. Typically it could be used for measuring the porosity of high end spec castings.

    The ?detector? as such is a mass spectrometer. Despite its very high level of efficiency it is also potentially the most expensive because of the equipment needed.

    I saw it used by Carrier many years ago in Syracuse where they were testing Absorption system unishells. The whole machine would be wrapped in a plastic ?tent? and a measured amount of helium admitted to it. A vacuum pump would then draw a vacuum on the inside of the system and the exhaust of the pump would be directed through a mass spectrometer.

    Not a technique for your average site??.
    ________
    marijuana vaporizers
    Last edited by Argus; 07-02-2011 at 08:09 AM.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Helium for leak detection

    Quote Originally Posted by chemi-cool
    Hi donhoban.

    Isn't the molecule of Helium smaller, allow the gas to come out in smaller holes then refrigerants?

    Peter, I haven't a clue but ultrasonic detector is very uncommon with fridgy's.

    Chemi
    I have an ultrasonic but it's only usable to search for leaks in gaskets around the doors.
    You must almost hear and know where the ***** leak is to find it with an ultrasonic.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Helium for leak detection

    Surely if we start using Helium for leak detection we are going to all start talking like Joe Pasquale

    Regards

    Raymond

  10. #10
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Helium for leak detection

    Quote Originally Posted by chemi-cool
    ...but ultrasonic detector is very uncommon with fridgy's.
    True, but I recommend it as a very valuable tool under some conditions. I finally broke down and bought one a few years ago when a leak was driving me crazy. They had come down to about $200. Mine uses earphones and supplies a hiss in the hearing range proportional to what the detector is receiving, with a sensitivity adjustment.

    They are excellent when a system is out of gas, since that usually means a large leak which overwhelms most halide detectors. Of course the oil often shows such a leak, or you can find it quickly by pressurizing with nitrogen and listening for the hiss, but when this fails, the best feature of the ultrasonic detector is that you can use it directionally.

    You need to pressurize with nitrogen if the system is empty and shutdown fans and adjacent equipment to eliminate background ultrasonics but then you can home in on the source very quickly, in many cases. With a thumb on the sensitivity adjustment, you track the noise right to the source. Last time, I found a leak in the interior of an evaporator coil in minutes, which was losing about 2 ounces per day. (Pressurized to 100 psi first.)

    For very small leaks and on rooftops where there is too much background ultrasonic noise (wind, traffic) it is not effective.

    Rog
    Last edited by RogGoetsch; 06-09-2004 at 07:49 PM.

  11. #11
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Helium for leak detection

    The more the technology advances the more tests needed , the more atmospher polluted the more tests needed .
    Unfortunably high tec technics are still very expensive to use by small and medium companies . . . the goverments should support the price of such testing materials in order to develope their countries industries and their contribution in the atmospher clearness preservation
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

Similar Threads

  1. 12VDC CO2 and Helium compressors??
    By permafrost in forum Transport
    Replies: 2
    Last Post: 21-08-2006, 12:06 AM
  2. Law and Leak detection
    By Bakerbj in forum Fundamentals
    Replies: 6
    Last Post: 21-03-2006, 10:39 PM
  3. Cost effective Freezer/Cooler Fire Detection
    By Marvin in forum New Technologies
    Replies: 6
    Last Post: 14-12-2004, 09:20 PM
  4. Gas detection
    By Mark in forum Supermarket Refrigeration
    Replies: 27
    Last Post: 08-08-2004, 07:04 PM
  5. Helium
    By Mike Hopkins in forum Refrigerants
    Replies: 3
    Last Post: 26-04-2002, 01:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •