    Re: Helium for leak detection



    What about PED regulations which states much higher testing pressures (+/- 25 bars on high side in most occasions)


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #52
    Join Date
    Apr 2001
    Location
    Southern England
    Age
    66
    Posts
    123
    Rep Power
    24

    Re: Helium for leak detection

    PED = Design and Manufacture

    Proof Test with Nitrogen or Argon (cheap and no environmental issues)
    Leak Test at max operating pressure (limit pressure al la PED) with helium as it gives a quantifiable result if done in a chamber.

    PSSR (UK) = Operation and Maintenace

    Leak Test with helium and portable mass spectrometer (£16K) again gives a quantifiable result if elak is above background levels (10e-6 m.bar.lt.sec-1).

    Washing Up liquid = corrosive salts and water will fill small porosities under capilary action and give false results but thats in the molecular leak rate zone.

    Nitrogen Under water = corrosion risk and water will fill small porosities under capilary action and give false results but thats in the molecular leak rate zone.

    Snoop or leak Detection Fluid = Not corrosive and viscious so pretty relaible for laminar leaks.

    Ultrasonic = Excellent in plant rooms not good for low pressure slow leaks and won't pick up oil signature from temperature/vibration activated leaks. No quantifibale display!

    Capacitive hand helds pick up every thing from cleaning solvents to bad breath but give users 'confidence' frequent 'ghost leaks' in plant rooms. No quantifibale display!

    Beta source detectors relaible but radiation hazard means hassels at end of the warranty period. Gives ppm and mass per year.

    IR Sensors good but bulky usually wall mounted and access by tubes making it slow to respond. Displays in ppm not mass per year.

    New HFC legislation

    This will mandate leak detection hand held for inspection.

    Just the rantings of a few years trying to find Nirvana and missing it.....
    Derek

Page 2 of 2 FirstFirst 12

Similar Threads

  1. 12VDC CO2 and Helium compressors??
    By permafrost in forum Transport
    Replies: 2
    Last Post: 21-08-2006, 12:06 AM
  2. Law and Leak detection
    By Bakerbj in forum Fundamentals
    Replies: 6
    Last Post: 21-03-2006, 10:39 PM
  3. Cost effective Freezer/Cooler Fire Detection
    By Marvin in forum New Technologies
    Replies: 6
    Last Post: 14-12-2004, 09:20 PM
  4. Gas detection
    By Mark in forum Supermarket Refrigeration
    Replies: 27
    Last Post: 08-08-2004, 07:04 PM
  5. Helium
    By Mike Hopkins in forum Refrigerants
    Replies: 3
    Last Post: 26-04-2002, 01:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •