    exp valve



    Hello all

    Can you use an externally equalised exp valve as an internally equalised one if you blank off the 1/4 port with cap ?

    regards

    Bernard



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: exp valve

    NO!


    Chemi

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: exp valve

    What do you think would happen if it was fitted

    bernard

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: exp valve

    You can, however use an externally equalized TEV to replace an internally equalized TEV. Simply connect the equalizing line to the evaporator outlet and it will operate fine.

  5. #5
    shogun7's Avatar
    shogun7 Guest

    Re: exp valve

    The constant pressure or automatic expansion valve responds to outlet pressure. It meters liquid refrigerant to the evaporator, maintaining a constant evaporator pressure. Refrigerant flows at a rate that exactly matches compressor capacity, and the valve incorporates a diaphragm that separates atmospheric pressure and system pressure with a range spring with an adjustable pressure setting is located above the diaphragm.
    Beneath the diaphragm is a stainless steel push rod and ball assembly backed by a closing spring with an o-ring located on the push rod creates a balanced port. This feature balances out the effect of increasing or decreasing inlet pressure, and aids in maintaining a constant outlet pressure. IMPORTANT..An equalizer passageway is incorporated into the valve body and this is what you don’t have on a TXV. So if you insist on using a TXV you need to drill an equilizing passageway. This can be done but you need to talk to the mfg for the right size drill

  6. #6
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: exp valve

    I'm with Chemi

    NO

    Just get the right valve I mean £20 !!!???

    There are three main forces in an ext equ. TEV the spring and the equalising line pressure to shut it and the bulb pressure to open it. The main closing force is the equalising line pressure.

    GET THE RIGHT VALVE
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: exp valve

    Inspired by Dan's post, you'd be convenienced to remember that if the evaporator consists of multiple parallel circuits then it'd be fed by a distributor which can have its own pressure drop normally much greater than the evaporator's pressure drop, with this application type you MUST use an externally equalised valve.
    I remember posting a reply in one thread stating that I was taught that a "rule of thumb" way to remember about TEV's was that if the system had a distributor then you should fit an externally equalised TEV. I also remember that this remark was not widely accepted as true

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: exp valve

    Quote Originally Posted by frank
    I remember posting a reply in one thread stating that I was taught that a "rule of thumb" way to remember about TEV's was that if the system had a distributor then you should fit an externally equalised TEV. I also remember that this remark was not widely accepted as true
    I do the same Frank, anyway installing a TEV with an eq. line can't harm never. It just cost a little bit more.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: exp valve

    hello blue boy

    Its not a question of money,it was curiosity and to confirm something I,ve seen on site.

    regards bernard

  10. #10
    shogun7's Avatar
    shogun7 Guest

    Re: exp valve

    Quote Originally Posted by frank
    I remember posting a reply in one thread stating that I was taught that a "rule of thumb" way to remember about TEV's was that if the system had a distributor then you should fit an externally equalised TEV. I also remember that this remark was not widely accepted as true
    Frank you are correct! In fact on an R-22 system distributer the pressure drop can be an average of 35 psi

  11. #11
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: exp valve

    Quote Originally Posted by frank
    I remember posting a reply in one thread stating that I was taught that a "rule of thumb" way to remember about TEV's was that if the system had a distributor then you should fit an externally equalised TEV. I also remember that this remark was not widely accepted as true
    I personally think it is a pretty good rule of thumb and one I have always found to be true!!
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  12. #12
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: exp valve

    OH I see Bernard I did not mean to apear bolshy. It does not change my answer however
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  13. #13
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: exp valve

    I remember posting a reply in one thread stating that I was taught that a "rule of thumb" way to remember about TEV's was that if the system had a distributor then you should fit an externally equalised TEV. I also remember that this remark was not widely accepted as true
    Hmmm. Don't know why that would be so, Frank. It's actually a little more than a reule of thumb. Sporlan Bulletin on distributors:

    When selecting a thermostatic expansion valve (TEV) for
    use with a Sporlan type distributor, an externally equalized valve must be used to compensate for the distributor
    pressure drop.
    BULLETIN 20-10

  14. #14
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: exp valve

    I think I understand, Marc. Your observations regarding hunting, and possibly flooding are very interesting and plausible, whereas, I would normally expect only evaporator starving to occur with an improperly applied internally equalized valve. I believe your friend's scenario is what happens when we try to compensate for that starving with TEV adjustments.

  15. #15
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24

    Re: exp valve

    Quote Originally Posted by Marc O'Brien
    None the less, "we" (in the trade) often come across evaporators being fed by just 2, 3 or 4 distributor tubes which are fed off of a plain short straight length of pipe fitted without a distributor nozzle. These system sometimes come from the factory without externaly equalised TEV's.
    These header arrangements generally do not create much pressure drop, and as a result, an internally equalized TEV can be expected to control a reasonable superheat with them. But that assumes the header is distributing refrigerant well, which will often not be the case. A hunting TEV can be expected.

    If you have more than the equivalent of a 2°F pressure drop across the evaporator coil, your best bet is to use an externally equalized TEV. A multi-circuited evaporator with a conventional distributor will require an externally equalized

    As the Prof recalls, Sporlan played around with internally equalized TEVs having thermostatic charges that were compensated for distributor pressure drop for Carrier in the 1960s. The problem with this approach is pressure drop across the distributor varies as the load varies, causing the TEV to flood at light loads and starve at high loads, making it not much more effective than a capillary tube.
    Prof Sporlan

  16. #16
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24

    Re: exp valve

    Quote Originally Posted by Marc O'Brien
    See, even the distributor tubes themselves require to be fed equally and so a distributor nozzle is employed to establish even distribution to the distributor tubes. In the tested application mentioned above, where the total distributor assembly's pressure drop is 25psi we are likely to find that the distributor nozzle's pressure drop is 18psi while the remaining pressure drop through the tube(s) is 7psi. Now, if the internally equalised TEV is closing because it see's a low "apparent" superheat on account of distributor and evaporator pressure drops, it is likely to affect a system capacity loss well in excess of 15%. The resulting reduced nozzle pressure drop, responding in proportion to the square of the remaining capacity factor, can very easily result in uneven distribution to the distributors and so to the evaporator, making valve hunt likely and floodback possible.
    If the distributor is sized for a 35 psi pressure drop at nominal conditions, the internally equalized TEV will invariably need to be adjusted all the way out to attempt to compensate for this pressure drop.

    Starving can be expected. Since distributor pressure drop is roughly proportional to the square of the refrigerant mass flow as noted above, disrtibutor pressure drop can fall well below expected values which can lead to distribution problems, hunting, and possibly some flooding.
    Prof Sporlan

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: exp valve

    Quote Originally Posted by Marc O'Brien
    Funny thing is, he turns over nearly as much as we do, the man has balls
    Turning over a lot is not that difficult, it's what remains in the wallet that counts if I made myself clear.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •