    exp valve

    Hello all

    Can you use an externally equalised exp valve as an internally equalised one if you blank off the 1/4 port with cap ?

    regards

    Bernard

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: exp valve

    NO!


    Chemi

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: exp valve

    What do you think would happen if it was fitted

    bernard

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: exp valve

    You can, however use an externally equalized TEV to replace an internally equalized TEV. Simply connect the equalizing line to the evaporator outlet and it will operate fine.

  5. #5
    shogun7's Avatar
    shogun7 Guest

    Re: exp valve

    The constant pressure or automatic expansion valve responds to outlet pressure. It meters liquid refrigerant to the evaporator, maintaining a constant evaporator pressure. Refrigerant flows at a rate that exactly matches compressor capacity, and the valve incorporates a diaphragm that separates atmospheric pressure and system pressure with a range spring with an adjustable pressure setting is located above the diaphragm.
    Beneath the diaphragm is a stainless steel push rod and ball assembly backed by a closing spring with an o-ring located on the push rod creates a balanced port. This feature balances out the effect of increasing or decreasing inlet pressure, and aids in maintaining a constant outlet pressure. IMPORTANT..An equalizer passageway is incorporated into the valve body and this is what you don’t have on a TXV. So if you insist on using a TXV you need to drill an equilizing passageway. This can be done but you need to talk to the mfg for the right size drill

  6. #6
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: exp valve

    I'm with Chemi

    NO

    Just get the right valve I mean £20 !!!???

    There are three main forces in an ext equ. TEV the spring and the equalising line pressure to shut it and the bulb pressure to open it. The main closing force is the equalising line pressure.

    GET THE RIGHT VALVE
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •