    I maintain some Thermo King refrigeration units which Use R403b refrigerant. This is a blend containing R22 and was a drop in replacement for R502 (r.i.p)
    Presumably then this will not be available past the end of this year. Can any one therefore suggest a replacement that does not require changing from mineral oil to POE?
    Any help or your experiences will be most gratefully received.
    Am I also right in thinking that I will not be able to use any virgin R403b after the end of the year.
    Jan 2009
    Serbia
    49
    30
    Re: Replacement for R403b
    Iwork TK unit SDII MAX,and I replace R403b with R404a and change oil.Other solution I dont know
    JohnO's Avatar
    JohnO Guest
    You are right that virgin R403B will not be available from the end of the year as it is a HCFC.
    You have several options if you want to stay on mineral oil: R422A (Isceon 79) or R428A (RS52) are probably the best options.
    Both are compatible with mineral oil and both suitable replacements for low temperature refrigeration. Capacity-wise, R428A has slightly better capacity than R422A and looking at my tables, should match R403B closely at -30 C. It also has negligible glide (0.5 C) which always helps!
    Pressures are similar to R403B (slightly lower)
  1. R22 replacement
    By brad__34 in forum Refrigerants
    Last Post: 04-06-2010, 09:06 PM
  2. Replacement Chiller Barrel Selection
    By archibaldtuttle in forum Air Conditioning
    Last Post: 09-06-2009, 08:09 PM
  3. Ranco K14 replacement
    By sturgm in forum Technical Discussions
    Last Post: 30-08-2008, 06:09 PM
  4. Replacement Screw Compressors
    By dkemper in forum Technical Discussions
    Last Post: 13-10-2007, 07:22 PM
  5. F 11 replacement for flushing
    By andrewuk in forum Refrigerants
    Last Post: 17-10-2003, 11:03 PM