    Question Getting More out of geothermal



    I have a question that has been vexing a number of my associates. If a compressor's refrigeration capacity in cooling is for instance 36,000 btu at maximum refrigerant mass flow, according to the manufacturer of the compressor, how is it possible that a geothermal heat pump's manufacturer has an output higher than that of the compressor, depending entering liquid temperature on the ground loop side.

    The calculation of btu/hr most commonly used by manufacturers of forced air geothermal heat pumps is:

    btu = delta T (across refrig air coil) x cfm x 1.08

    Thanks to all who reply.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Getting More out of geothermal

    The heat output of a condenser is the refrigeration capacity (heat absorbed in the evaporator) plus the heat of compression.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Getting More out of geothermal

    Quote Originally Posted by Popper View Post
    I have a question that has been vexing a number of my associates. If a compressor's refrigeration capacity in cooling is for instance 36,000 btu at maximum refrigerant mass flow, according to the manufacturer of the compressor, how is it possible that a geothermal heat pump's manufacturer has an output higher than that of the compressor, depending entering liquid temperature on the ground loop side.

    The calculation of btu/hr most commonly used by manufacturers of forced air geothermal heat pumps is:

    btu = delta T (across refrig air coil) x cfm x 1.08

    Thanks to all who reply.

    When you talk about the duty of a refrigeration system, you are talking about the work done over the evaporator.

    With a heat pump you are talking about the work output of the condenser, The out put is the input of the evap and the duty of the compressor.

    Hope this helps.

    taz.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Getting More out of geothermal

    Generally referred to as COP, coefficient of performance. Energy in verus energy out.

Similar Threads

  1. Geothermal Closed Loop Question
    By Backhertz in forum New Technologies
    Replies: 5
    Last Post: 28-10-2008, 08:04 PM
  2. Small Geothermal Heat Pump
    By EDDC in forum Heat Pumps
    Replies: 5
    Last Post: 17-07-2008, 07:38 AM
  3. Geothermal heat pumps
    By dhananjaylagwan in forum Fundamentals
    Replies: 9
    Last Post: 19-04-2008, 02:24 PM
  4. Bryant geothermal heat pump dehumidfier
    By Backhertz in forum New Technologies
    Replies: 0
    Last Post: 16-03-2008, 02:44 AM
  5. geothermal heat pump
    By goodguy in forum Heat Pumps
    Replies: 18
    Last Post: 06-02-2008, 10:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •