    Calculation of absorbed R-134a in compressor oil



    I have been developing a refrigerant charge calculation procedure for a heat-pump circuit.

    The part that currently needs some work is that for an estimate of the mass of R-134a refrigerant absorbed by the compressor POE oil.

    If anyone has links to a suitable reference article, or link, I would be most grateful.

    -----------
    Practical test:
    During a vacuum pump-down of my lab heat-pump, prior to re-gassing, I listened to the compressor (scroll) as the vacuum pump began pulling. The sound of gas bubbling was very evident. As the vacuum level increased, the base of the compressor became cold (sweat) & reduced in temperature off atmospheric, by around 15'C. The sweat line was some 70% of the distance from base to suction inlet. The de-gassing phase took quite some time to complete.


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Calculation of absorbed R-134a in compressor oil

    I have a couple of pdf with some good info but cant find the link. Send me a PM with your email and I will send it to you.

    Chef

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Calculation of absorbed R-134a in compressor oil

    Quote Originally Posted by desA View Post
    Practical test:
    During a vacuum pump-down of my lab heat-pump, prior to re-gassing, I listened to the compressor (scroll) as the vacuum pump began pulling. The sound of gas bubbling was very evident. As the vacuum level increased, the base of the compressor became cold (sweat) & reduced in temperature off atmospheric, by around 15'C. The sweat line was some 70% of the distance from base to suction inlet. The de-gassing phase took quite some time to complete.
    I'm guessing the entire charge found its way to the compressor while the system was off.
    Last edited by Gary; 27-07-2009 at 04:56 AM.

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Calculation of absorbed R-134a in compressor oil

    Quote Originally Posted by Chef View Post
    I have a couple of pdf with some good info but cant find the link. Send me a PM with your email and I will send it to you.

    Chef
    Thanks, Chef.

    PM sent, including e-mail address.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Calculation of absorbed R-134a in compressor oil

    The pdf's are sent. you may also like to look at this

    http://findarticles.com/p/articles/m...g=content;col1

    It has all the calculations you need but is a bit hard to follow.

    Chef
    Last edited by Chef; 27-07-2009 at 11:11 AM. Reason: Clarity

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Calculation of absorbed R-134a in compressor oil

    Quote Originally Posted by Chef View Post
    The pdf's are sent. you may also like to look at this

    http://findarticles.com/p/articles/m...g=content;col1

    It has all the calculations you need but is a bit hard to follow.

    Chef
    Thanks so much for the articles. I'll continue per e-mail on the specifics.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Calculation of absorbed R-134a in compressor oil

    Quote Originally Posted by Gary View Post
    I'm guessing the entire charge found its way to the compressor while the system was off.
    I tend to agree with you. The unit had stood for some time & was de-gassed directly off this storage position.

    The off-gassing sounded like fluid flowing inside the compressor shell, at first. The give-away was the temperature drop in the shell as the refrigerant gassed off.

    All very interesting & got me thinking about how much gas is actually generally entrained in the compressor oil during operating conditions. The main reservoir is estimated to be in the compressor shell (scroll-type), due to its 'accumulator-type' design.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Calculation of absorbed R-134a in compressor oil

    When a system is off, the refrigerant will migrate to the coolest point, which is usually the evaporator.

    If the suction line is a straight run downwards to the compressor, the refrigerant will be delivered by gravity to the compressor.

    For this reason it is good practice to have the suction line go up to the top of the evaporator and then down to the compressor. This traps the liquid in the evaporator.

    But if the compressor should become the coolest part of the system the trap won't stop the refrigerant from migrating to the compressor.

    If this is a possibility then a crankcase heater is added to prevent the compressor from becoming the coolest part of the system.

Similar Threads

  1. how can we calculation industrial refrigeration
    By lam sanh in forum System Optimization
    Replies: 34
    Last Post: 28-02-2011, 01:31 PM
  2. Need Help in Refrigeration Calculation
    By Jason_09 in forum Fundamentals
    Replies: 7
    Last Post: 30-06-2009, 07:10 PM
  3. Refrigeration Capacity with R 134a
    By Samarjit Sen in forum Refrigerants
    Replies: 7
    Last Post: 02-06-2009, 02:28 AM
  4. Calculation bypass buffer tank volume
    By abbasi in forum New Technologies
    Replies: 3
    Last Post: 16-10-2008, 06:19 AM
  5. Replies: 3
    Last Post: 27-11-2007, 10:00 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •