    Re: Urgent: absorption chiller

    Quote Originally Posted by weatherman View Post
    What type of machine are you talking about. Is your refrigerant water? is your absorbant lithium bromide?

    YES , its water/LiBr

  2. #2
    Join Date
    Apr 2008
    Location
    england
    Posts
    8
    Rep Power
    0

    Re: Urgent: absorption chiller

    Quote Originally Posted by nostalgia View Post
    YES , its water/LiBr
    If the machine has been running at low load for a long time the water may be contaminated with lith/brom this needs to be reconstituted. You may have to add some octy alchol to the water,The steam or hot water needs to be at the machine design temp and the condenser/absorber water needs also to be at design to ensure correct operation. Take samples of refrigerant and lithd/brom and check consentrations