Results 1 to 9 of 9
Thread: Vacuum Cooling
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2007
    Hampshire
    438
    32
    Vacuum Cooling
    Hi All
    Could someone assist in shedding some light.
    Cooling in a vacuum is achieved by boiling water, mostly off the surface of the product to be cooled.
    At 0°C, the saturation pressure is around 0.6 kPa.
    Water vaporizes in the chamber under the low pressure. Until saturation is achieved. To increase saturation levels a condensing coil is fitted in the chamber.
    What is the temperature required at 0.6 kPa for condensing to take place?
    Why does water not flash off again as run off from the condensing coil occurs?
    Any insight much appreciated.
    Scotland
    327
    Re: Vacuum Cooling
    The chamber is being maintained at saturation point and will be vapourising and condensing on all surfaces. There is no flashing off as such. Assuming your figures are correct, then the temperature required is therefore 0 c.
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Re: Vacuum Cooling
    Thanks but I would assume that there is some subcooling required on the condenser below saturation temperature.If water is vaporising at 0.
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Re: Vacuum Cooling
    At 6.5 mBar (5 Torr) water is boiling at 0 c.
    Does anyone have a chart or nomograph for water at low pressures ie 10 - 0 Torr.
    Apr 2001
    79
    5,071
    35
    Re: Vacuum Cooling
    When a liquid/vapor is at saturation, adding heat will cause the liquid to change to a vapor or removing heat will cause the vapor to change to a liquid. During this change of state, in either direction, it will remain at saturation temperature.
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Re: Vacuum Cooling
    Yes but to achieve condensation you have to change the state of equilibrium. With a condensing coil in the vacuum chamber heat given up is the latent heat of sublimation. Sublimation occurs when air saturated with water vapor is suddenly cooled below the freezing point of water.
    My question is if water is vaporizing at 0 C what would be the required condensing temperature?
    Apr 2001
    79
    5,071
    35
    Re: Vacuum Cooling
    Quote Originally Posted by hookster View Post
    The required condensing temperature would be 0 C.
    Apr 2001
    79
    5,071
    35
    Re: Vacuum Cooling
    Okay, to elaborate on this:
    The source of heating must necessarily be more than 0 C, and the source of cooling must be less than 0 C, but the change of state is at saturation temperature (0 C).
    Scotland
    327
    Re: Vacuum Cooling
    It is vapourising and condensing (BOILING) at the same time at constant pressure and temperature. There is no sub cooling and no superheat. Sub cooling can only be achieved when 100% of the refrigerant is below saturation point (latent heat of condensation). The refrigerant can only be superheated when 100% of the refrigerant is above saturation point (latent heat of evaporation).
    The conditions you describe are no different to a pot of boiling water at 100 c in your kitchen. Only the pressure has changed.
  1. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Last Post: 08-08-2008, 05:13 PM
  2. Compressor loading, cooling, and range of operation.
  3. Vacuum test
    By Peter_1 in forum Fundamentals
    Last Post: 13-10-2006, 09:04 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Last Post: 13-10-2005, 05:14 AM