    F Gas Log Books



    Hi

    We are using a sheet similar to Defra's example but it is not great. There are not enough spaces for leak teak test dates and each sheet will be full after 2 years.

    I am wondering if we can supply this sheet and on each maintenance visit write on the engineers report sheet 'all systems leak checked'.

    Has anyone got a better way of record keeping?



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: F Gas Log Books

    .

    DEFRA's example is one that shows a typical format with the minimum information needed to comply with the F Gas laws.

    That's all it is - an example.

    You could make your own in excel, say, and add as many field as you think appropriate for the equipment, then extend it over time to show what you have done on each visit. You can add as much space as you need.


    .

  3. #3
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: F Gas Log Books

    I opened the example sheet in word rather than pdf, you can add a few extra spaces to the boxes to fit more stuff in. The example i have now is about 4 pages long.

  4. #4
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: F Gas Log Books

    Do you think we really need to fill in this log book/sheet for every system, every time a maintenance visit is carried out. If you have given the customer a report which reads 'all systems leak checked' this should suffice.

    I find companies are doing it in different ways and none seem to compare very well.

  5. #5
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: F Gas Log Books

    Quote Originally Posted by R1976 View Post
    Do you think we really need to fill in this log book/sheet for every system, every time a maintenance visit is carried out. ..............

    .



    In a word - yes, if you do anything to open the system, add or remove refrigerant or carry out a mandatory leak check.

    There's a great deal of detail on DEFRA and BERR's web sites.

    Start with this page that tells you what reporting is necessary:

    http://www.defra.gov.uk/environment/...ly/records.htm


    It is your customer's responsibility (he's the 'operator') to make sure that the records are kept, but he's paying you to do the work and provide the information.

    It's your name and your company's, together with your registration details that should appear on the records each time you do something to the system.


    .

  6. #6
    Join Date
    Sep 2008
    Location
    Letsby Avenue
    Posts
    359
    Rep Power
    17

    Re: F Gas Log Books

    Would have thought that Defra should have issued the form free so that everyone works of the same sheet then we are all doing the same record keeping.
    Have hardly met one comsumer who knows their responsibility in this,always ends up me pointing them to the legislation.

Similar Threads

  1. books needed
    By rich74310 in forum Refrigeration Books
    Replies: 0
    Last Post: 15-06-2009, 07:10 PM
  2. Books about single-screw compressor
    By DVaider in forum Refrigeration Books
    Replies: 8
    Last Post: 16-05-2007, 07:34 AM
  3. RETA books
    By lana in forum Refrigeration Books
    Replies: 16
    Last Post: 09-05-2007, 12:19 PM
  4. Air conditioning Books
    By Student Eng in forum Refrigeration Books
    Replies: 2
    Last Post: 20-03-2006, 11:35 AM
  5. Books for Ammonia Design
    By lana in forum Refrigeration Books
    Replies: 1
    Last Post: 28-10-2005, 02:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •