Large Air handling Equipment Dehumidification / Litres Per Hour ?
Hi guy's
I'm just new here so bear with me so as I can get up to speed please !
My question is I've been on line looking for information
re : air handling equipment calculation's and the amount of moisture removed, but cannot find anything really that gives me litres per hour rates !
Doe's anyone know where to go to find this out does Trane have any spec's on their equipment ?
" Hope you can help ! "
Deluxairhead
-
26-07-2009, 02:31 PM #2
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
Is this on a system already running? I ask because you can plot the temperature and humidities of air on and air off on a psychrometric chart to get the moisture removal.
www.compactaircon.co.uk
-
27-07-2009, 01:17 PM #3
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
The equation for calculating kg/hr is :
kg/hr = (Vol x delta kg/kg x 3600)/ sp Vol
where:
Vol = Volume of air (m3/s)
Delta Kg/kg = Difference in Moisture content of air before and after cooling process
3600 = Constant to convert between Hr/sec
sp Vol = (Specific Vol(start) + Specific Vol(finish))/2
All details obtained from Psychrometric Chart
-
05-08-2009, 10:21 AM #4
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
Hi guys
Thanks for the heads up Frank I think I'll be able to get a calculation together, cheers again !
Wayne / Deluxair
-
05-08-2009, 09:12 PM #5
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
Thanks for the response/feedback Wayne.
-
09-08-2009, 04:57 PM #6
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
You can plot entering or leaving conditions on a chart
You can also convert latent cooling capacity into mositure removed.
Take about every 1060 btu of latent heat as a pound of condensate.
Not into converting to joules and kg for you at the moment. itTake the V out of HVAC and you are left with a HAC job
-
09-08-2009, 06:31 PM #7
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
To make progress is never good enough, I want to do better and better and better
-
09-08-2009, 06:37 PM #8
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
A bucket and a stop watch?
-
09-08-2009, 07:18 PM #9
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
yes that's right Gary
To make progress is never good enough, I want to do better and better and better
-
09-08-2009, 08:27 PM #10
-
10-08-2009, 02:03 PM #11
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
Frank,
If you can measure the volume flow at the inlet of the cold coil at a know temperature you already know the mass flow. Then based on the temperature and H.R. on point 1 and point 2 you can calculate the massflow of moisture that goes out (condensed water).
I'm sorry I didn't understand what you mean with "there is a difference (kj/kg) on the mass flow lines".
kg is kg of dry air not total mass.To make progress is never good enough, I want to do better and better and better
-
17-08-2009, 06:35 PM #12
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
You can find detailed instructions in my book on how to calculate the process line of an air conditioning system on a psychrometric chart. The book is HVAC Design Manual – A Mechanical Designer’s Guide to Design of Small Commercial and Institutional HVAC Systems and is available for free download at my web site, www.nettally.com/doughert. See chapter 7 for psychrometric calculations and how to avoid moisture problems in an air conditioned building.
The replies you already received are correct, so what you will get from my book is a more complete guide to psychrometrics.
-
17-08-2009, 06:48 PM #13
Re: Large Air handling Equipment Dehumidification / Litres Per Hour ?
Or you can use a bucket and a stop watch.