    scotsman mv600 fault



    All i feel i do is ask questions about ice machines on here


    Anyway heres the story hope someone can set me on the right track

    Its a scotsman mv600 and its a solid light on bin full. Now i have been all over this unit and cant see how its possible for it to know when the ice bin is full, no sensors that i can see.

    On initial start up it fills the water up and runs the compressor as it fills, on older models i remember the water was actually pumping round the ice cups before going onto refrigeration mode??
    So it runs for around 10 seconds then returns to bin full warning.

    Its got a full charge of 404a in there so shouldn't be tripping out on lp or hp unless switches are out of range.

    Im starting to think the controller may be at fault, would like to see if any engineers who know these machines better than me can add anything before i make the hasty desicion of ordering a new pcb board.

    Also can some one explain to me how the magnetic switch operated on these?



  2. #2
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    ok just found this and found some interesting information
    http://www.doorgeestkoeltechniek.nl/....2012-2004.pdf


    The magnetic switch controls the switchin of the freezing cycle.

  3. #3
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    Bin full warning light = inoperative or faulty magnetic switch

    looks like i might have solved it!

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: scotsman mv600 fault

    scotsman also used a limit switch on the water cover located top left hand side.
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: scotsman mv600 fault

    there is a bin sensor on that machine, try taking side pannels off

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: scotsman mv600 fault

    the micro switch is a bin sensor as well.being that when cover is held open as in no more ice can fall,board times out quickly and led is lit.on one job found the cover was jamming against back of the machines front panel,customer thought he was the fonz,give it a whack and away it goes.
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    Quote Originally Posted by mcunliffe4 View Post
    there is a bin sensor on that machine, try taking side pannels off

    which panel as i have had side panels top panel and front panel off and traced all wires from controller?

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: scotsman mv600 fault

    Quote Originally Posted by Colin G View Post
    which panel as i have had side panels top panel and front panel off and traced all wires from controller?
    There is no bin sensor.

    Its all about the plastic deflector in front of the evaporator. If the deflector does not return to the closed position after the ice sheet drops, the magnetic switch does not start the next cycle and the machine thinks the bin is full.

    Keep in mind that the deflector closes by gravity. If the machine is not level (leaning forward) gravity does not close the deflector. Make sure the machine is level, or maybe even leaning backwards slightly.

    If the deflector is closing properly, clean the magnet surface. It must make solid contact to activate the magnetic switch. If all else fails, replace the switch.
    Last edited by Gary; 25-07-2009 at 06:06 PM.

  9. #9
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    Quote Originally Posted by Gary View Post
    There is no bin sensor.

    Its all about the plastic deflector in front of the evaporator. If the deflector does not return to the closed position after the ice sheet drops, the magnetic switch does not start the next cycle and the machine thinks the bin is full.

    Keep in mind that the deflector closes by gravity. If the machine is not level (leaning forward) gravity does not close the deflector. Make sure the machine is level, or maybe even leaning backwards slightly.

    If the deflector is closing properly, clean the magnet surface. It must make solid contact to activate the magnetic switch. If all else fails, replace the switch.
    i see, its all starting to make sense to me now
    i have ordered a new switch so will try the above before replacing, thanks for that.

  10. #10
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: scotsman mv600 fault

    Before ordering a switch remove the ice flap and place a magnet on the switch and see if it cuts everything in, we use our solonoid lifting magnetic coils very handy for this sort of thing and we also use them on magnetic door switches.
    Grumpy men live longer

  11. #11
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: scotsman mv600 fault

    sorry mate thinking of a different cabinet, gary's rite check magnetic switch on curtain

  12. #12
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: scotsman mv600 fault

    magnetic switch on the curtain definatley. this is used for bin full. dont like it much prefer a proper bin sensor/stat but hey technology moves on

  13. #13
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    i dont think there is a curtain, the cube cups sit vertically on this unit and the water runs down them, the magnetic switch is to the bottom left screwed onto the ice cube section, im heading back in there tomorrow so will have another looky see

  14. #14
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: scotsman mv600 fault

    its more of a plastic panel than a curtain but it prevents water from entering the bin and is hinged at the top so it moves as the ice gets thicker once the sensor breaks the machine will go on harvest/defrost until the ice has dropped and the sensor remakes.

  15. #15
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16

    Re: scotsman mv600 fault

    Quote Originally Posted by 1mikeefc1 View Post
    its more of a plastic panel than a curtain but it prevents water from entering the bin and is hinged at the top so it moves as the ice gets thicker once the sensor breaks the machine will go on harvest/defrost until the ice has dropped and the sensor remakes.
    the ice thickness sensor? this is situated half way up the face of the evap and has 2 metal levers that push out with the ice?

  16. #16
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: scotsman mv600 fault

    ice bridge thickness sensors ive seen usually are mounted from top right hand from centre of evap and swings forward freely
    mmm to beer or not to beer...........lets drink breakfast

  17. #17
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    79
    Posts
    195
    Rep Power
    17

    Re: scotsman mv600 fault

    I have seen ice machines wher the small magnet in the cover has broken or fallen out. You can just stick another small magnet in the hole. Not very sure if this was a Scotsman problem or another make of machine.

Similar Threads

  1. YORK YAEP recip chiller fault
    By chiller1 in forum Trouble Shooting
    Replies: 8
    Last Post: 04-06-2010, 10:41 AM
  2. scotsman acm125 fault
    By skeggyboy in forum Trouble Shooting
    Replies: 6
    Last Post: 15-07-2009, 06:23 PM
  3. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •