    Post Short of Gas in R404 serve over



    I recently went to a job and found 2 seperate condensers short of gas, I also found the condensers blocked with dust and flour as they were in a bakery the gas was R404a, I leak testedthe system and found no leaks in the system so weighed in my gas a they ran perfectly, I was wondering due to the blocked condensers I know this might be stupid but would the gas boil off and is that why there is a shortage of gas as there was def no leaks in the system.



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Short of Gas in R404 serve over

    I presume you reclaimed it out so it's a simple matter of out v in difference isn't it?

    However gas doen't boil off liquid does, but yes if it can't condense then it can't boil off again..

  3. #3
    Join Date
    Oct 2007
    Location
    Northern Ireland
    Age
    41
    Posts
    13
    Rep Power
    0

    Re: Short of Gas in R404 serve over

    Sorry yes I did reclaim so there is a possibility the liquid could boil of

  4. #4
    Join Date
    Aug 2008
    Location
    uk
    Posts
    22
    Rep Power
    0

    Re: Short of Gas in R404 serve over

    regardless of the state of the refrigerant there should be the same amount in as was originally charged unless there is a leak, some cowboys will let charge out to lower head pressures rather than looking at the cause, ie blocked condenser, poor ventilation etc, maybe that's what happened?

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Short of Gas in R404 serve over

    Quote Originally Posted by shills33 View Post
    I recently went to a job and found 2 seperate condensers short of gas, I also found the condensers blocked with dust and flour as they were in a bakery the gas was R404a, I leak testedthe system and found no leaks in the system so weighed in my gas a they ran perfectly, I was wondering due to the blocked condensers I know this might be stupid but would the gas boil off and is that why there is a shortage of gas as there was def no leaks in the system.
    If the condensors were blocked then you wouldnt get good heat rejection so the discharge vapour may not fully condense in the condensor, meaning you would get liquid and vapour at your metering device.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Short of Gas in R404 serve over

    if you have a severely blocked condenser you might have some micro leaks on the system that cant handle the high HP. I would re charge system with arglow leak dye to cover yourself and show up any leaks in the future if no pressure drop seen using OFN.



  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Short of Gas in R404 serve over

    If condenser was blocked and yet could put in more gas could mean micro leaks which could surface later .
    If the refrigerant has not leaked out , system would refuse to accept further gas as it would reflect on discharge pressure

Similar Threads

  1. appears short of refrigerant
    By TECH TIM in forum Commercial
    Replies: 11
    Last Post: 11-02-2009, 11:48 AM
  2. R404
    By Giannis in forum Refrigerants
    Replies: 22
    Last Post: 13-02-2008, 08:41 PM
  3. SCR short in soft starter.
    By mrsparky in forum Electrical
    Replies: 0
    Last Post: 14-12-2007, 12:19 PM
  4. Walk in Cooler (short cycling)
    By Brandon in forum Trouble Shooting
    Replies: 11
    Last Post: 05-05-2003, 11:43 AM
  5. using R404 to chill watermixture
    By fredperry in forum Technical Discussions
    Replies: 21
    Last Post: 21-05-2002, 10:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •