Thread: Flow Rate through Fan Coil Unit
-
20-07-2009, 06:47 AM #1
Flow Rate through Fan Coil Unit
Is their any way to calculate the actual flow rate through the FCU when the design & Actual Parameters are as....
System Installed with Auto Flow Valve with a catridge for 0.23L/sec requires a minimun differential pressure of 19 Kpa for the specified flow rate as recommended by Manufacturer.
Design Flow Rate: 0.23 L/s
Measured Diff. Press. across Auto Flow Valve: 79Kpa
Coil Pressure drop (frm Manufacturer): 8.28 Kpa
Measured Pressure Drop at Coil: 13.20 Kpa
Please advise how to calculate actual flow rate through the coil?
Thanks for helps.
-
20-07-2009, 10:41 PM #2
Re: Flow Rate through Fan Coil Unit
If your auto-valve is working then your flow rate is 0.23l/s.
The fpressures at the coil would indicate a higher flow rate but are the pressure test points the manufacturers test points or your own?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-07-2009, 04:52 AM #3
Re: Flow Rate through Fan Coil Unit
-
21-07-2009, 05:31 AM #4
Re: Flow Rate through Fan Coil Unit
Get an annometer and check for yourself the actual air flow.
magoo
-
21-07-2009, 06:42 AM #5
Similar Threads
-
AHU Calculations
By SUBCONTRACTOR in forum FundamentalsReplies: 20Last Post: 07-11-2009, 04:51 AM -
Simple off-coil temperature for Fan Coil Unit in Heating.
By robertheppell in forum FundamentalsReplies: 11Last Post: 20-05-2009, 06:26 AM -
LG heat pump problem
By back2space in forum Heat PumpsReplies: 132Last Post: 01-02-2009, 11:23 PM -
Efficiency of compressor assisted HRV
By montreal in forum Heat PumpsReplies: 46Last Post: 27-08-2007, 08:51 PM -
Selecting Evaporator coil and condensing unit
By Abe in forum Tools and CalculatorsReplies: 7Last Post: 04-04-2003, 03:20 PM