    r407c



    R407c
    Is it true that if you have a leak on a R407c unit,you have to reclaim the gas and put a fresh charge in?I was under the impression that 407 is not diffrent to any r400 gases.Ie charge as a liquid,due to it been a blend.But some one told me today that you cannot add gas to a 407 system,is this true?
    {after you have fixed the leak of cause}.



  2. #2
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: r407c

    hellloooo
    as you were saying r407c is one of the 400 series which has to be charged as liquid , when it leaks yo dont know how much of which refrigerant has leaked out.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: r407c

    Some test in field are done and it is safe to top-up of about 10-20% of total charge without significant change in performance.
    If you need to top up more than that, you should recover and recharge with new refrigerant.

  4. #4
    Join Date
    Nov 2007
    Location
    Kent
    Age
    49
    Posts
    7
    Rep Power
    0

    Re: r407c

    If you have a leak with a R407c you should always reclaim the refrigerant and then recharge with fresh gas, R407c is basicly R410A with some R134A thrown in, If you have a small leak on the system you will generally lose the R134A as this has a very fine molecular structure and you will have something that resembles R410A in the system. Quite often I have found R407c systems running with high HP's due to the systems having a small leak normally on the suction side.

    There is a school of thought that if the leak is on the Liquid side of the system you should lose the blend in equal amounts but I never trust this.

    I had a call from a customer yesterday with a HP fault on one of our systems and after talking to him and getting to check gas pressure's and more importantly temperatures he reclaimed the system and found it 6kg's short (total charge is around 30kgs) the leak was found and the system recharged and ran perfectly.

Similar Threads

  1. r22 used in r407c rooftop unit.
    By just joe in forum Air Conditioning
    Replies: 11
    Last Post: 23-07-2008, 01:35 PM
  2. R407C Questions
    By marwanm in forum Refrigerants
    Replies: 8
    Last Post: 02-04-2008, 09:46 AM
  3. R407c
    By binman54 in forum Refrigerants
    Replies: 3
    Last Post: 16-12-2006, 10:57 PM
  4. R407C to R404a
    By MaDiNfO in forum Air Conditioning
    Replies: 10
    Last Post: 30-07-2006, 09:34 AM
  5. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •