    Is their any way to calculate the actual flow rate through the FCU when the design & Actual Parameters are as....
    System Installed with Auto Flow Valve with a catridge for 0.23L/sec requires a minimun differential pressure of 19 Kpa for the specified flow rate as recommended by Manufacturer.
    Design Flow Rate: 0.23 L/s
    Measured Diff. Press. across Auto Flow Valve: 79Kpa
    Coil Pressure drop (frm Manufacturer): 8.28 Kpa
    Measured Pressure Drop at Coil: 13.20 Kpa
    Please advise how to calculate actual flow rate through the coil?
    Thanks for helps.
    69
    10,501
    Re: Flow Rate through Fan Coil Unit
    If your auto-valve is working then your flow rate is 0.23l/s.
    The fpressures at the coil would indicate a higher flow rate but are the pressure test points the manufacturers test points or your own?
    deepu's Avatar
    deepu Guest
    Test points are not by manufacturer for the Coils and are provided in the installed pipework and value includes additional pressure drop in the pipework. Measured Pressure drop across Auto FLow Valves are using the manufaturer test points/locations.
    Auckland
    67
    3,362
    31
    Get an annometer and check for yourself the actual air flow.
    magoo
    deepu's Avatar
    deepu Guest
    magoo
    Thanks,
    I am looking for... how to calculate actual water flow rate through the coil?
  1. AHU Calculations
    By SUBCONTRACTOR in forum Fundamentals
    Last Post: 07-11-2009, 05:51 AM
  2. Simple off-coil temperature for Fan Coil Unit in Heating.
    By robertheppell in forum Fundamentals
    Last Post: 20-05-2009, 06:26 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Last Post: 02-02-2009, 12:23 AM
  4. Efficiency of compressor assisted HRV
    By montreal in forum Heat Pumps
    Last Post: 27-08-2007, 08:51 PM
  5. Selecting Evaporator coil and condensing unit
    By Abe in forum Tools and Calculators
    Last Post: 04-04-2003, 03:20 PM
Tags for this Thread