    How many changes of the volumen of a Room must one change per hour in order garantee room conditions?
    Thanks
    Gwapa



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Air Changes in a Refrigerated Room

    I think your question is not very clear. It shall depend on the application & nature of persons present in the Room.

  3. #3
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Air Changes in a Refrigerated Room

    A freezer at -28ēC to storage fruit pulp how many air changes should have?

    A freezer at -28ēC to storage fish (tune) how many air changes should have?

    A refrigerated room at +5ēC to storage milk and butter How many air changes should have?

    A storage meat room ?

    A procesing meat room with people inside at 10ēC?

    This are some applications

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Air Changes in a Refrigerated Room

    I have never heard if using "x" air changes per hour for refrigerated spaces. This is typically only used for occupied rooms (processing, etc) and not for product storage.

    If anything, I would be more concerned with air throw and spread.

    Air throw is the distance the air will travel. At this distance the terminal air velocity is achieved. Some evaporator manufacturers may list the air throw but they may not list the terminal velocity. If not, you should ask them.

    The terminal velocity is important because you may need a sufficient air flow over the product. Air throw is important since you need to provide air flow to an adequate distance.

    Spread is how far the air spreads out. Think of it as a isosceles triangle. The point of the triangle is the center of the fan. The base of the triangle is the spread at the required distance. As the air leaves the fan tips the air starts to decelerate and mix with the room air. This deceleration causes the air to spread out from the radial flow it started with.

    If you provide a sufficient quantity of evaporators that are installed to circulate a uniform terminal velocity at the required distance with the spread providing adequate coverage, you should be good to go!
    If all else fails, ask for help.


  5. #5
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Air Changes in a Refrigerated Room

    US ICEMAN
    I agree with you .However I found the attached file as a part of a Handbook of a Manufacturer .

    I couldn´t achive to such figures It look to me very high.

    What I know is that lowering the TD I will increase the air flow required for the same load

    But this figures in the attached file look to me wrong

    Could you please comment
    Best regards
    Gwapa


    Attached Files Attached Files

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Air Changes in a Refrigerated Room

    Quote Originally Posted by gwapa
    I couldn´t achieve to such figures It look to me very high.
    Not without using a lot of fan power I bet!

    I would not worry about air TD, only the evaporator TD. Pick the coils for what you want to achieve.

    If the cooling capacity is too high the air TD will be lower also.

    Seriously, I don't know where those numbers came from. That is a lot of air to circulate...

    What book did you find that in? I agree with everything except the air changes.
    If all else fails, ask for help.


  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Air Changes in a Refrigerated Room

    What is the story about?

    I couldn´t achive to such figures It look to me very high.
    Quite contrary, the figures in that table should be very low for your total cfm multiplied by 60/ volume of your cold room.
    The formula is inadequate and they stress it themselves. How had they come (and how one should) to the figures in the table they did not explain.

  8. #8
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Air Changes in a Refrigerated Room

    Probably the Air changes word is more confusing. Typically the air flow quantity in the cold stores / freezers should be based on these factors.

    So many a times even if you get less air flow by your calculations, may be you have to ensure that still the Air quantity is as per the table.

    We have come across these situations many a times, & in a floriculture applications these tables are not useful as the flowers get damaged due to high velocity.

  9. #9
    Join Date
    Jan 2009
    Location
    lleida
    Age
    50
    Posts
    47
    Rep Power
    0

    Re: Air Changes in a Refrigerated Room

    Hi,
    the only thing i can say is that these factors are important to know for storage of vegetables specially fruits or products that can get damaged for high air speed across the product wich causes dehidration (water loss).
    But this means also that the product must be correctly "stored" in the room.
    I mean that the owner must kepp some distances beetwen pallets (if it's the case) to allow the air pass through the product at a velocity slow enough.
    Also you must be sure that the air is not by-passing to the evaporator without passing through the product.
    I would not take care only of having a minimum air in the room but also at hese other factors.
    I hope these ideas are useful.

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Air Changes in a Refrigerated Room

    Hi,


    ... this is coefficient of air circulation i.e total volume of empty chamber which must pass through the cooler/s in one hour ....


    all is logical... for work areas/cutting rooms very small 20-30 changes/hour and for blast freezer 150-300 giving a clearer idea of air movement.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. Thawing Room (defrosting Room For Meat)
    By arunuae in forum Commercial
    Replies: 3
    Last Post: 09-02-2008, 09:24 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •