    screw compressor high discharge temp



    we have an oil flooded screw compressor for propylene refrigeration service that trips frequently on high discharge temperature(78 deg c, ) (usually when the plant is running at turndown)what changes do u guys think can be made to lower the discharge temperatures(lowering suction pressure,increasing economizer duty etc). I have also noticed that propylene coming to the compressor from the evaporators is sometimes highly superheated at the suction conditions. what could be the possible reason? is this the correct forum or should i be posting somewhere else?



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: screw compressor high discharge temp

    Daredevil,

    Propylene (glycol?) superheated??

    +78ºC is not a high discharge temperature. check the operating limits of the screw compressor and check the setpoints of the controller.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Oct 2010
    Location
    new delhi
    Age
    36
    Posts
    7
    Rep Power
    0

    Re: screw compressor high discharge temp

    no c3h6 propylene. the vendor of the refrigeration package has provided a trip on high compressor discharge temp 78 deg C.
    what i meant was at the compressor inlet saturated propylene should have a temp of about -15 deg C at suction pressure of 3.5 bara according to our simulations...but weve found this is much higher upto 0 deg C

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: screw compressor high discharge temp

    Quote Originally Posted by daredevil View Post
    no c3h6 propylene. the vendor of the refrigeration package has provided a trip on high compressor discharge temp 78 deg C.
    what i meant was at the compressor inlet saturated propylene should have a temp of about -15 deg C at suction pressure of 3.5 bara according to our simulations...but weve found this is much higher upto 0 deg C
    A high superheat could result on higher discharge temperatures...of course the magnitude depends on the refrigerant used. For example for ammonia this fact is very important.

    Does the evaporator is been well fed? Also if there is a high pressure drop on the all suction line that would "help" to get higher superheated vapor at the compressor inlet.
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: screw compressor high discharge temp

    discharge temperature is a function of suction gas temp and the pressure ratio (discharge / suction pre). both these should be relatively lower if you want to lower the discharge gas temperature. not sure if this helps...

    Is propylene a refrigerant in screw? I have not heard before. other forum people may be knowing better.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: screw compressor high discharge temp

    I had never heard of it before, but Mr Google says its R1270 propene[ propylene] made by Linde.

  7. #7
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: screw compressor high discharge temp

    Propylene not far off propane. Mixture of (2) called MAP gas....

    What lubricant being used and how is it cooled? Many of the higher suction pressure hydrocarbons do not require very much cooling at peak loads but depending on the compressor and oil circulation will need considerable cooling at low loads....And the oil cooling determines your discharge temp; the 2-temperatures should track each other or even be nearly identical depending on how your are cooling the oil as well as how you are managing its flow...