    Raise evap temp 1 degree better effic



    the ample questions for 2079 say if evap temp raised 1 degree c eff improve 3% where can i get some background reading to understand this or can someone expalin please??



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Raise evap temp 1 degree better effic

    Hi, gwm121

    welcome to RE forums...

    Quote Originally Posted by gwm121 View Post
    the ample questions for 2079 say if evap temp raised 1 degree c eff improve 3% where can i get some background reading to understand this or can someone expalin please??
    sorry my English is not that good ... but, please, search RE forums ... keywords like cop, c effective, energy saving, condensing temp/press .... etc.... and for sure you'll find something about ... something about min/max dt over heat exchanger - evaporator or condenser ... why to increase suction temp/press and decrease condensing temp/press to get better COP i.e. decrease energy consumption... limits regarding sizes of evaporators/condensers due to manufacturing costs ...

    or you can wait .... for sure someone will come to explain it in better English language than my

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Raise evap temp 1 degree better effic

    The refrigerant is also more dense as pressure /temp increases .
    This will mean compressor can pump more volume of gas , so increases its efficiency .
    Basically you want highest suction pressure / temp to achieve room/product temp .

  4. #4
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: Raise evap temp 1 degree better effic

    it's a bit of a buzz word at the moment "suction optimisation" have a look on the danfoss web site ... at least i think thats what you are looking for

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Raise evap temp 1 degree better effic

    if evap temp raised 1 degree c eff improve 3% where can i get some background reading to understand this or can someone expalin please?
    Imagine a task of transferring of 10 packs from one room to another. By that, the first pack weighs 10 kilograms, the second weighs 10% more than the first, the third 10% more than the second, etc.

    One begins with the lightest pack, then carry the pack which is 10% heavier, etc.

    By every go one makes 10% more work but his muscles may consume, let's say, only about 3.3% more energy. 10/3.3 = about 3% increase in efficiency.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Raise evap temp 1 degree better effic

    This is for me not a good question: it depends on so many things
    1. Refrigerant used
    2. Evaporating pressure
    3. In which region are we working: freezing, cooling or AC application? Extremely important
    4. There's nothing said about the condensing pressure.

    Possible good answers could be the following but only to judge if the candidate gets the point of this question:
    1. 3% (the good answer according to those who made it but not necessarily the only one)
    2. -3%
    3. 10%
    4. 0%

    But giving 2 %, 2.5%, 3% and 3.5% as possible good answers isn't correct. I can give pressures and/or situations where all answers will be true.

    I've seen other F-gas questions which aren't correct for me.
    Last edited by Peter_1; 21-07-2009 at 10:46 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Raise evap temp 1 degree better effic

    The same is also valid when lowering HP
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Raise evap temp 1 degree better effic

    Hi GWM121,

    I think that you need to plot it on a PH chart to clarify, on the right hand side you will see lines of constant specific volume, as the specific volume increases through lower suction pressures or excess superheat the mass flow reduces and so does system efficiency.

    Cheers
    Tutto il Mondo e un Paese

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Raise evap temp 1 degree better effic

    Assuming a basic system, there are two opposing forces in the evaporator which balance against each other. The heat load pushes the pressure/temperature up while the compressor pulls the pressure/temperature down.

    If the pressure/temperature rises as a result of increased heatload the system runs more efficiently, moving a lot more heat for a little more energy.

    If the pressure/temperature rises as a result of the compressor not pulling as hard as it should (broken valves for example) then the efficiency drops like a rock, moving a lot less heat for a little less energy.

    Its not the bang and its not the buck. Its the bang for the buck.
    Last edited by Gary; 21-07-2009 at 05:25 PM.

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. planning/setting evap temp with cap tubes
    By kubae in forum Commercial
    Replies: 2
    Last Post: 14-10-2007, 02:08 PM
  4. Endless Freezer as Endless Cooler (10 door)
    By herefishy in forum Commercial
    Replies: 95
    Last Post: 17-04-2002, 12:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •