    P Traps at Evaps



    Ok guys, try this one, my apprentice asked me today why do we come out of and evap into a P trap and then go through the cold room ceiling into another inverted one. With the new gases and our knowledge of refrigerant flow velocity and volume and the amazing quality of oil separators available is there any need !!!! I said liquid he said suction accumulator! Bloody apprentices I said I'd ask you guys


    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: P Traps at Evaps

    Why the inverted trap on the ceiling?Never did and saw this.
    The linee must just have a slope towards the compressor, that's all.

    P trap under the evaporator is to ensure proper oil return.
    I rarely install them. If it's less then 3 ft, then we just install a smaller section upwards.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: P Traps at Evaps

    Hi Blueboy
    on flooded applications traps are rarely fitted, oil return is either by the hot gas during defrost or thru careful selection of the pipe sizes to ensure proper velocities, 10m/sec comes to mind.
    I would say with the oils we use now, POE. PAO and AB oil return traps are less important.
    Better still to use traps were part load operation is envisaged, say a main suction riser on a pack or a mains suction fed by a number of rooms that of-cycle.
    I suppose the old story, better safe than sorry, it's a lot easier to let the oil get there than to remove it.
    Kind Regards. Andy

  4. #4
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: P Traps at Evaps

    hmm So then to summarise!! Our considered option is as the apprentice said with new gasses and correctly sized pipe and well commissioned plant with correct components (good oil sep and suction accumulator may be) a P after the evap and certainly the one above is not required
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: P Traps at Evaps

    Hi blueboy
    maybe not required, but still good practice to fit a p trap at the evaporator. We tend to use pump-down, so little liquid is present to affect the bulb on start up.
    I would say modern evaporators have nicely fabricated header which are traps in themselves. All the same I would still fit a trap.
    Kind Regards. Andy.

  6. #6
    shogun7's Avatar
    shogun7 Guest

    Re: P Traps at Evaps

    On a system where there is a direct drop to the condenser a "P" trap is not necessery, however, when the cond unit is above the evap then you should use a "P"trap for 2 reasons
    1. On lite loads oil will tend to accumulate in the evap and should drain in "P" trap then as load increases mass velocity will increase in trap threby helping to facilitate oil return.
    2. It helps to make sure that no liquid refrigerant is in contact with sensing bulb especially after a defrost

Similar Threads

  1. Oil Traps in risers
    By Jasper in forum Air Conditioning
    Replies: 20
    Last Post: 10-06-2010, 11:26 PM
  2. Spectrum evaps ex-valve settings
    By nova in forum Transport
    Replies: 6
    Last Post: 22-06-2004, 04:01 PM
  3. U Traps
    By frank in forum Technical Discussions
    Replies: 14
    Last Post: 04-05-2004, 08:51 PM
  4. multiple evaps
    By angryk in forum Fundamentals
    Replies: 5
    Last Post: 28-12-2003, 09:49 PM
  5. Recirculations ammonia evaps
    By Friobernal in forum Fundamentals
    Replies: 5
    Last Post: 03-04-2003, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •