    What Suction Pressure do i need?



    Hi all

    I was wondering what suction pressure i should be looking for will trying to achieve a room temperature 0 degrees celscius.

    The system runs on R22 and feeds 2 T.E.Vs and 2 coolers.
    The charge in the system is approx 20kg


    If anyone can help that would be great!



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: What Suction Pressure do i need?


  3. #3
    Join Date
    Jul 2008
    Location
    England
    Age
    39
    Posts
    31
    Rep Power
    0

    Re: What Suction Pressure do i need?

    Thanks Gary but i will explain my problem a little more

    When doing my refrigeration course i was taught if i dont know the weighted charge a system holds, fill it until the sight glass on the liquid line is full, no bubbles or flashing etc.

    Due to a very hot couple of weeks here in the UK we had a sub-contractor in our factory helping out. The system in question had lost its charge, after the leak was repaired he re-charged the system.
    Now whilst charging he said he noticed the room set point was 0 degrees C. But while having a suction pressure of 3.5 bar he was reluctant to put more charge in until the sight glass was clear. Saying that while having this suction pressure we would never achieve the set point. He has not been back since.

    Now do i reclaim some of the gas put into the system, alter the set point to something more achievable or check the superheat, i am however reluctant to alter the superheat until im sure thats the cure.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: What Suction Pressure do i need?

    Do not touch the TEV, it is not at fault.

    Read Gary's link.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: What Suction Pressure do i need?

    Quote Originally Posted by Mish View Post
    Hi all

    I was wondering what suction pressure i should be looking for will trying to achieve a room temperature 0 degrees celscius.

    The system runs on R22 and feeds 2 T.E.Vs and 2 coolers.
    The charge in the system is approx 20kg


    If anyone can help that would be great!

    R22 at 0 deg C is about 5 b so if you have evap at -10 deg C then back pressure will be about 3.5 b.

    taz.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Suction pressure for R22 3 ton reci chiller
    By jayaeros in forum Trouble Shooting
    Replies: 2
    Last Post: 12-09-2008, 11:22 AM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •