    404 freezer wont go all the way down



    im from norway ,pronounces english like an mental nutcase.

    i have a never ending history with an accona freezer bench.customer claims the temperature isnt low enough only -13 celsius he wont -18. set temp is -22
    .system is ,404a 1000gram ,danfoss sc12,te2 00 orfice .compressor and condenser is supposed to be in the funiture(bench) but is moved out to other room 27celsius ambient .7meter tubing 1/4" 3/8".it has a reciever as well.

    first time suction pressure seemed high 1.8 bar gauge.and tev didnt compensate .called my refrigerant supplier, he recommended me to change tev and orfice .at that moment i didnt know it was fitted with orfice 00 (not sure if that is original)so when i told him compressor size and desired cabinet temp he suggested the 0x orfice .

    after replaced tev and orfice 0x temp stay the same .but suction pressure is 1 bar gauge .the i have may overlooked is the condensing temp in the middle of the condenser pipetemp is 27celcius and headpressure is 12,5 bar (after reciever) and head pressure goes down when temp goes down in cabinet.sightglass is full and clean but liquidline is "cold" maybe 20 celcius

    btw compressor is replaced filterdrier and burnout filter. flushed with nitro and in a long vacum

    could the 0x orfice be to small to this evap ,no heat to reject or maybe condenser fit better ambients in the bench

    or does it need exorcism?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404 freezer wont go all the way down

    If the ambient is 27C, then the liquid line cannot be 20C, unless there is a restriction between the condenser and the point where you determined that the line was 20C.

    But then, we don't know if the line was 20C, because that was just a guess.

    If we are going to help you, we don't need guesses or opinions, we need real temperature and pressure measurements.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404 freezer wont go all the way down


  4. #4
    cold viking's Avatar
    cold viking Guest

    Re: 404 freezer wont go all the way down

    Quote Originally Posted by Gary View Post
    If the ambient is 27C, then the liquid line cannot be 20C, unless there is a restriction between the condenser and the point where you determined that the line was 20C.

    But then, we don't know if the line was 20C, because that was just a guess.

    If we are going to help you, we don't need guesses or opinions, we need real temperature and pressure measurements.
    ok i agree with you that maybees wont go anyway .but if i ask you what can cause an not warm liquid line and low head .as long as compresor is new and i have charged gas with weight and 50gram additional for tubing 7m

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404 freezer wont go all the way down

    If the system absorbs little heat from the evaporator, then it has little heat to reject in the condenser.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404 freezer wont go all the way down

    If the system has the proper charge and the new TXV is properly sized, but the coil is starved, then there must be a liquid line restriction (or plugged coil inlet/distributor/equalizer line). Did you replace the drier? Is the TXV externally equalized?
    Last edited by Gary; 16-07-2009 at 10:47 PM.

  7. #7
    cold viking's Avatar
    cold viking Guest

    Re: 404 freezer wont go all the way down

    Quote Originally Posted by Gary View Post
    If the system has the proper charge and the new TXV is properly sized, but the coil is starved, then there must be a liquid line restriction (or plugged coil inlet/distributor/equalizer line). Did you replace the drier? Is the TXV externally equalized?
    i replaced the drier , the txv is not externally equalized .the coil could defently be starved due to the smaller orfice .since compressor is moved i added 40gram for the 7metres longer piping. it has reciever
    just added charge to have it close as possible to original spec.superheat spindle is all out and 3 turns in that should be factory setting.are going to measure superheat and subcooling

    if we assume that 0x is to small for evap and i swith to 00 orfice could that possibly raise my head enough

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404 freezer wont go all the way down

    Before I made any judgements about the system, I would get a full and accurate list of temperatures and pressures.

    Evap air in temp
    Evap air out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet

    Cond air in temp
    Cond air out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet

  9. #9
    Join Date
    Mar 2009
    Location
    South Africa
    Posts
    43
    Rep Power
    0

    Re: 404 freezer wont go all the way down

    Gary is right as always. Full set of readings.

    But with my limited experience I'd say that the orifice is way too small. LP at -30degC with a cabinet at -13degC. The original figure of 1.8bar LP was much closer.

    But listen to Gary, he really knows his stuff.

  10. #10
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: 404 freezer wont go all the way down

    If you know the details of the compressor then you need to find out it's capacity and then determine your orifice size, the scale is on the inside of the danfos txv box, once you know you have the right valve and orifice, then you can start looking at your pressures, no point guessing. Like Gary said, the condenser will only start working if the evap is working. SOunds like a case of just getting back to basics. (An MOP valve hasn't been installed by mistake has it, i've seen that before)

  11. #11
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: 404 freezer wont go all the way down

    Quote Originally Posted by cold viking View Post
    just added charge to have it close as possible to original spec.superheat spindle is all out and 3 turns in that should be factory setting.
    This is incorrect setting turn adjusting screw fully clockwise then out 2 1/2 turns anticlockwise this is factory setting. You should not mess about with the tev adjustment screw it is rarely required.
    Transvestites are men who like to eat, drink, and be Mary.

Similar Threads

  1. Blast Freezer Within Freezer
    By rickmor in forum Technical Discussions
    Replies: 4
    Last Post: 18-06-2009, 03:37 AM
  2. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  3. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  4. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  5. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •