    modifying ashp? Evaporator question



    The ashp's have a large flat area evaporator. Is there any reason why they cannot be a smaller surface area but more layers (if you know what I mean)

    Sorry, I'm an installer not a techie!

    thank you for any guidance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: modifying ashp? Evaporator question

    Probably to do with the heat transfer rate.

    Compare an air conditioner coil and a freezer coil and the number of rows within them.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: modifying ashp? Evaporator question

    The ashp's have a large flat area evaporator. Is there any reason why they cannot be a smaller surface area...
    The main reason for current evaporator designs being so large is that they are based on archaic heat-transfer technology. Plate-fin + tube evaporator assemblies are incredibly inefficient in terms of overall performance. The main reason for their continued manufacture seems to be their relatively low cost.

    I have a new technology project in the R&D phase, where we plan to reduce the current evaporator volumes by at least 50%. This development has the potential to be a disruptive (industry-changing) technology. The heat-transfer side has a few small technical tricks to be smoothed, but, in principle it is doable.

    So the answer to your question is that within the next few years, it is possible that evaporators will drastically reduce in footprint & volume.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Mar 2009
    Location
    South Africa
    Posts
    43
    Rep Power
    0

    Re: modifying ashp? Evaporator question

    I'll just post bits from a table I got from our coil manufacturer.

    On a 2 row coil:
    1st row does 57% of the work
    2nd row does the remaining 43% of the work

    6 row coil:
    Row 1 to 3 does 66% of the work
    Row 4 to 6 does 34% of the work

    10 row coil:
    Row 1 to 5 does 66% of the work
    Row 6 to 9 does 32% of the work
    Row 10 does 2% of the work

  5. #5
    northbridge's Avatar
    northbridge Guest

    Re: modifying ashp? Evaporator question

    Thank you for that table, it answers a lot of questions.

    I have a unit that we need to modify into a smaller package, so am looking at smaller evaporator, increased fanspeed/

    here goes!

Similar Threads

  1. ashp as primary heating source ?
    By Essex1968 in forum Heat Pumps
    Replies: 8
    Last Post: 02-08-2010, 05:32 PM
  2. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Replies: 3
    Last Post: 10-10-2008, 07:28 AM
  3. modifying a commercial reachin
    By tempered in forum Technical Discussions
    Replies: 2
    Last Post: 10-03-2007, 02:32 AM
  4. Modifying cabinet temps
    By james in forum Fundamentals
    Replies: 16
    Last Post: 01-05-2002, 08:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •