modifying ashp? Evaporator question
The ashp's have a large flat area evaporator. Is there any reason why they cannot be a smaller surface area but more layers (if you know what I mean)
Sorry, I'm an installer not a techie!
thank you for any guidance.
-
16-07-2009, 10:43 PM #2
Re: modifying ashp? Evaporator question
Probably to do with the heat transfer rate.
Compare an air conditioner coil and a freezer coil and the number of rows within them.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-07-2009, 02:43 AM #3
Re: modifying ashp? Evaporator question
The ashp's have a large flat area evaporator. Is there any reason why they cannot be a smaller surface area...
I have a new technology project in the R&D phase, where we plan to reduce the current evaporator volumes by at least 50%. This development has the potential to be a disruptive (industry-changing) technology. The heat-transfer side has a few small technical tricks to be smoothed, but, in principle it is doable.
So the answer to your question is that within the next few years, it is possible that evaporators will drastically reduce in footprint & volume.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
17-07-2009, 07:46 AM #4
Re: modifying ashp? Evaporator question
I'll just post bits from a table I got from our coil manufacturer.
On a 2 row coil:
1st row does 57% of the work
2nd row does the remaining 43% of the work
6 row coil:
Row 1 to 3 does 66% of the work
Row 4 to 6 does 34% of the work
10 row coil:
Row 1 to 5 does 66% of the work
Row 6 to 9 does 32% of the work
Row 10 does 2% of the work
-
18-07-2009, 07:34 AM #5
Re: modifying ashp? Evaporator question
Thank you for that table, it answers a lot of questions.
I have a unit that we need to modify into a smaller package, so am looking at smaller evaporator, increased fanspeed/
here goes!
Similar Threads
-
ashp as primary heating source ?
By Essex1968 in forum Heat PumpsReplies: 8Last Post: 02-08-2010, 05:32 PM -
Modifying aricond. for heating, cooling and hot water
By kimusabi in forum Technical DiscussionsReplies: 3Last Post: 10-10-2008, 07:28 AM -
modifying a commercial reachin
By tempered in forum Technical DiscussionsReplies: 2Last Post: 10-03-2007, 02:32 AM -
Modifying cabinet temps
By james in forum FundamentalsReplies: 16Last Post: 01-05-2002, 08:49 PM