    What would be the normal low side and high side pressures on a R22 air conditioning system with the folowing parameters

    Ambient 30 Degrees Celcius
    Remote Controller set at -16C




  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34
    Pressures are only meaningful when converted to saturation temperature, and even then they represent only a small part of the refrigeration or A/C picture.

    If you want to understand what's going on in a system, you need the following:

    High side saturation temp.
    Condenser air in temp.
    Condenser air out temp.
    Liquid line temp at receiver outlet.
    Liquid line temp at TXV inlet.
    Low side saturation temp.
    Evaporator air in temp.
    Evaporator air out temp.
    Suction line temp near compressor inlet.
    Suction line temp at TXV sensing bulb.

    All of these variables affect pressures.


  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60
    As Gary correctly said there is a lot a information required before you can state what is correct for a given system.

    However, think on this - you are only trying to cool air not freeze it so what 'range' of low side pressures would you expect?

    Also, most important - - it doesn't matter a rat's ar*e what temperature the remote controller is set at
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    May 2001
    Location
    Los Angeles
    Posts
    23
    Rep Power
    0

    Wink

    Perhaps I missunderstand your aplication but here are some thoughts Abe. I asume your remote control is controlling the temp of the area to be cooled. -16c to me is a freezer which equates to 3.2F in the states. I usually figure a 10F degree TD thru the coil or the coil is 10 degress colder then the air. This means the coil would be -6.8F or -18.5C. look at the TP chart and see what preasure this is and check your gauges. Should be fairly close. If not check your superheat thru the coil. Of course there is preasure loss depending on piping but you can come close.
    Jack

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26
    Thank you Jack for your reply, stat is set at 16 c and not minus 16
    I have info now to go on so thanks a lot
    As they say you learn a little every day


    [Edited by Abe on 05-06-2001 at 10:37 PM]

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  2. Replies: 35
    Last Post: 13-12-2006, 12:51 PM
  3. Operating Theatres
    By nick_nst@aapt.n in forum Air Conditioning
    Replies: 6
    Last Post: 05-06-2006, 12:19 PM
  4. System Design Pressures
    By herefishy in forum Fundamentals
    Replies: 11
    Last Post: 27-01-2004, 01:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •