    R407c



    Is it true that if you have a leak on a R407c unit,you have to reclaim the gas and put a fresh charge in?I was under the impression that 407 is not diffrent to any r400 gases.Ie charge as a liquid,due to it been a blend.But some one told me today that you cannot add gas to a 407 system,is this true?
    {after you have fixed the leak of cause}.



  2. #2
    Join Date
    Jul 2006
    Location
    Romania
    Age
    43
    Posts
    99
    Rep Power
    18

    Re: R407c

    There is another thread with this subject.On cruise ships we use to charge over not to recover and recharge..
    Regards Mihai

  3. #3
    Join Date
    Aug 2008
    Location
    uk
    Posts
    22
    Rep Power
    0

    Re: R407c

    your about right, the glide on 407 makes it unwise to top up, i can't remember the amount you can lose before it's a full change, but if it's a good leak then i'd charge with virgin as the performance drops off dramatically, i'm sure someone can give you figures if you need them

  4. #4
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: R407c

    i was told that if the leak is from the high side then you can but if it's a low side leak then reclaim and recharge... reason being vapour no body knows what leaks out and what percentage of each leaks

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R407c

    I have heard this theory many times over the years, and I don't doubt that a leak in just the right place at just the right time could drain off one of the component refrigerants... but what effect would topping up the charge have on the actual operation of the system?

    I seriously doubt that the effect on the system's operation would be noticeable and have yet to see any evidence to the contrary. Surely someone somewhere has actually tested this.

  6. #6
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: R407c

    http://www.centrogalileo.it/nuovaPA/...%20inglese.doc

    This document is interesting. To paraphrase what it says, you CAN top up R407c on non-critically charged systems (ie. chillers), but split a/c systems are critically charged, so you would have to start again.

  7. #7
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: R407c

    Sorry, just tried the link and it's broken .... I'm rubbish on pc's.

    I tried to attach the document, but it exceeds the 100kb limit.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R407c

    If I am in fact wrong and zeotropes must be regassed rather than topped up, then where is the sense in using them? As a prime example R404A (zeotrope) is almost identical in composition and characteristics to R507 (azeoptrope). R404A can fractionate, while R507 cannot. This alone seems to make R507 the superior refrigerant.

  9. #9
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: R407c

    Difficult to tell what Gary has told you as he is on my ignore list. R407c is a blend, however i have recharged systems that have lost 70% charge as a vapour with no problems afterwards. I just use it like 22 with no problems. ( dont mix it with 22 though, that may be bad)
    Takes a licking, keeps on ticking.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: R407c

    Gary, there was (is?) on the website of Rhodia (France biggest refrigerant manufacturer) a technical paper saying that you always can top off R407c systems.
    Practical tests over years showed now difference.
    They shouldn't say this officially if they weren't 100% sure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: R407c

    Like Gary said, how does the blend know what part must leak out and what part must stay.

    What sometimes happens is that with a leak and maybe running your suction in a vacuum, you could add non condensebles and that could change the state and behaviour of the refrigerant, which are mistakingly blamed on the refrigerant.

    Never had the problem with blends, ****tails, whatever, as long as the system is not 90% empty. It is then a good idea to reclaim the charge, change oil and driers, vacuum and recharge.
    I am not always right, but I'm never wrong!

Similar Threads

  1. What gauges can i use for R407c????
    By luke.180 in forum Refrigerants
    Replies: 15
    Last Post: 29-01-2010, 07:50 PM
  2. r22 used in r407c rooftop unit.
    By just joe in forum Air Conditioning
    Replies: 11
    Last Post: 23-07-2008, 01:35 PM
  3. r407c chiller issue
    By Lc_shi in forum New Technologies
    Replies: 3
    Last Post: 09-01-2008, 01:22 AM
  4. R407c
    By binman54 in forum Refrigerants
    Replies: 3
    Last Post: 16-12-2006, 09:57 PM
  5. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •