Results 1 to 10 of 10
-
14-07-2009, 08:32 AM #1
need help for Tecumseh compressor
carrier Model: 48TJD006-501YA. 208/230V 3PH
Tecumseh Compressor Model: AVB5558EXT.200/220V 3PH
one year new
When I turn the A/C on, the compressor soundss very noise, and the suction line pressure is: 50psi. and high side pressure is: around 400psi. condenser air inlet and outlet is normal. and inside supply air is not cold enough. Can any technician tell me what is the problem? is something wrong with the compressor or somewhere stuck (block) in the high side? thank you very much
-
14-07-2009, 09:02 PM #2
Re: need help for Tecumseh compressor
And... the refrigerant is ??
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-07-2009, 09:12 PM #3
Re: need help for Tecumseh compressor
-
14-07-2009, 09:15 PM #4
Re: need help for Tecumseh compressor
Right on the spot Gary.
I think you should check first the fertibilisation.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-07-2009, 10:56 PM #5
Re: need help for Tecumseh compressor
You should need to blow out condenser coil and report back with results.
Transvestites are men who like to eat, drink, and be Mary.
-
22-07-2009, 11:29 PM #6
Re: need help for Tecumseh compressor
If the temperatures are indeed "normal" then it may be that you have none condesibles in your condenser reducing the capacity of it.
Either way...it sounds like you need a fridge dude.
-
26-07-2009, 09:44 PM #7
Re: need help for Tecumseh compressor
you replace your cappliry tube or expension valve
-
26-07-2009, 09:46 PM #8
Re: need help for Tecumseh compressor
you check your filterdrier is to warm or normal if its to warm your condenser is durty you clean and wash your condenser
-
27-07-2009, 02:44 AM #9
Re: need help for Tecumseh compressor
To repeat Brian UK's question...., the refrigerant is .. ? You have hundreds of possible options these days, just pick one.
Last edited by Magoo; 27-07-2009 at 02:46 AM. Reason: addition
-
05-08-2009, 07:21 PM #10
Re: need help for Tecumseh compressor
sounds like non condensibles in there, or perhaps a blocked condensor- slow or reverse direction condensor fan?
Similar Threads
-
Help needed to find a replacement compressor
By 540itouring in forum DomesticReplies: 19Last Post: 17-04-2010, 02:06 PM -
Lighting's affect on compressor load
By TeamESI in forum Tools and CalculatorsReplies: 0Last Post: 14-05-2009, 06:26 PM -
Thumping noise in the compressor
By Husky250 in forum Air ConditioningReplies: 6Last Post: 16-05-2008, 10:48 PM -
Compressor Knock problem
By AC90 in forum New to REReplies: 10Last Post: 11-05-2008, 04:26 PM -
screw compressor
By vinod in forum Trouble ShootingReplies: 9Last Post: 17-12-2005, 01:46 AM