    Pump out accumulator on an HP Float system (ammonia)



    Has anybody have a quick way or idea to pump out the suction accumulator on an HP float system as the receiver is designed to transport liquid and not used for storage?


    Any ideas....



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Pump out accumulator on an HP Float system (ammonia)

    Then it becomes a large pipe?
    Surely you need a liquid seal within it.
    Or has what it supplies been disconnected?
    Sorry for being so thick.
    I can't see what you are trying to achieve?
    Grizzly

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    The only quick way is to have a spare liquid reciever or storage vessel to hold the whole charge .
    You only have a pilot type reciever so nearly all ammonia charge is in accumulator .

  4. #4
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    Grizzly, i don't think you know what im talking about mate, you totally off track.
    Last edited by benji; 14-07-2009 at 09:19 AM.

  5. #5
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    yes as well as in the evaporator, there is no other liquid receiver thats the problem, i can store it in the condenser cant i?

  6. #6
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    If i haven't mentioned, im changing the sight glasses on the level column on the accumulator.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    Would have thought that bullseyes could be isolatable , as well as high level switch .
    Would give it a thorough look before you do anything like empty accumulator .

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    There's not much chance of holding all the liquid in condensor either if you want to pump it down .

  9. #9
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Pump out accumulator on an HP Float system (ammonia)

    Most of the time the columns have hand valves to isolate them so you can change the sight glass, but if you dont you can put the ammonia anywhere in the system, evap coils, condenser. Is this wet or dry suction?

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Pump out accumulator on an HP Float system (ammonia)

    Quote Originally Posted by benji View Post
    Grizzly, i don't think you know what im talking about mate, you totally off track.

    Yes I was wasn't I.
    (it was am.)
    If you had said you needed to purge the accumulator to work on it.
    I would of understood!
    Do you have access to an ammonia reclaim unit?
    Using it to transfer to the high side.
    Don't use them myself.

    Just a thought!
    (As I don't know the system and don't want to get put down again. )

    Could you shut the liquid feed into the unit, running it.
    Having dropped the suction control pressure.
    This would then back the charge up into the condenser and the system.
    At least you should reduce the refrigerant in the accumulator.
    Until it cuts out on Low level or LP.
    I would assume that it is then a complete isolation of the accumulator.
    And purge off the remaining Ammonia (controlled through water of course).

    I also use a vacuum pump to eradicate any remaining vapour. Prior to opening up a part of the system.

    Hope it helps Grizzly

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pump out accumulator on an HP Float system (ammonia)

    Quote Originally Posted by benji View Post
    Grizzly, i don't think you know what im talking about mate, you totally off track.
    This is because your question is not complete or not complete enough. If you don't give us all the information, then we have to start guessing of course.
    I'm almost sure Grizzly has more experience then you have in this field.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    yes it is a dry suction

  13. #13
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    they installed the system with out bulls eyes, how stupid i try that thanks even if theres not much in the accumulator i can pump the rest out into water, thanks.

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump out accumulator on an HP Float system (ammonia)

    Benji.
    Ring me and we will discuss it. I know your system you are talking about. Bring cheque book as well.

    magoo

  15. #15
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    Thanks guys, job done apologize for the incorrect explanation. I shut the supply to the accumulator so now the economiser will start filling up and the plant will trip on economiser high level emptying the accumulator.

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump out accumulator on an HP Float system (ammonia)

    Benji.
    half right half wrong, the site glass leg has isolation vavs, and a pump-out vav on bottom vav. Why pumpout accumulator?. Old saying "look before starting".
    magoo

  17. #17
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Pump out accumulator on an HP Float system (ammonia)

    Hi, benji

    Quote Originally Posted by benji View Post
    Has anybody have a quick way or idea to pump out the suction accumulator on an HP float system as the receiver is designed to transport liquid and not used for storage?


    Any ideas....
    I saw your post where, fortunately, you solved your problem ... but with question like this one above ... we can have a lot of ideas and none will be good for you... why ... not enough input info and then we have to guess ....

    maybe I sound rude - sorry, I don't want that, but how we can help if we do not know what you need ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  18. #18
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    Quote Originally Posted by Magoo View Post
    Benji.
    half right half wrong, the site glass leg has isolation vavs, and a pump-out vav on bottom vav. Why pumpout accumulator?. Old saying "look before starting".
    magoo
    If this is FMC frigopak like in your pictures it does'nt make sense either

  19. #19
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    Quote Originally Posted by benji View Post
    Thanks guys, job done apologize for the incorrect explanation. I shut the supply to the accumulator so now the economiser will start filling up and the plant will trip on economiser high level emptying the accumulator.
    If this is a Frigopak like in your pictures ,it still does'nt make sense , how you filled up economizer and emptied accumulator ?
    If thats the case your plant is very short of NH3 and liquid pump would'nt
    would shut down on differential .

  20. #20
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump out accumulator on an HP Float system (ammonia)

    Ranger1
    It is a Frigopak, and I think we are only getting half the story.
    magoo

  21. #21
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    Which half ?

  22. #22
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    It is a frigo pak, the sight glasses are replaced so now i can see the levels in the system. The level of the refrigerant in the accumulator when there is no load is on the bottom sight glass, should it be?

  23. #23
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Pump out accumulator on an HP Float system (ammonia)

    If liquid reciever , economizer levels ok then room down to temp turn off fans .
    If liquid pump does'nt cavitate then nh3 charge ok .
    Possibly giving to much info away , sorry Magoo .

  24. #24
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    thanks will try that

  25. #25
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump out accumulator on an HP Float system (ammonia)

    Benji,
    All the points that Ranger1 suggested, and let system stabalize for 15 minutes. You should just see liquid inbottom sightglass. If it is full it is over charged. Double check after 15 minutes and manually load compressor to 100% for a short time, then unload again. You can watch it all on the screen. If pump does not cavitate, you are on the mark.

    Ranger1 this is probably too much info..

  26. #26
    Join Date
    Jan 2008
    Location
    newzealand
    Age
    47
    Posts
    44
    Rep Power
    0

    Re: Pump out accumulator on an HP Float system (ammonia)

    haven't tried that yet, i can only do it when production is not running, never the less on my checks this morning on start-up the micro-controller on the screen said Nh3 pump pressure low and then 15minutes after the pressure just picked up and then it was ok. However it always does this on start-up, suppose it stops cavitating when the liquid is at a lower temperature.
    Last edited by benji; 20-07-2009 at 09:18 AM.

  27. #27
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump out accumulator on an HP Float system (ammonia)

    Benji.
    The micro will ignore pump fluctuations during pull down, to avoid nuisance trips etc., The pull down will be slow for first start, as in minimum pulse load rates and reverts to rapid response once machine is 100% loaded.
    Last time I was there you had fully opened the oil feed valve to load cylinder, which gives big chunks of slide changes and agrivates the boiling effect in accumulator and pump cavitation. Pull down should take 50 minutes without product in freezer. Any quicker and you create problems for system and yourself,[ HP problems ] mainly the client.I also noted that the HP control point was changed, that can create more problems during normal production. Stop playing with things. This system is not a normal coldstore type application, that has one pull-down in its life, this system pulls down every day in its life, rapid pull down would need a condenser twice the size. Get the picture.
    magoo

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  3. Ammonia Absorption System
    By Samarjit Sen in forum NH3
    Replies: 13
    Last Post: 04-10-2006, 11:39 AM
  4. Ammonia Transfer System
    By gwapa in forum Fundamentals
    Replies: 7
    Last Post: 12-09-2006, 01:12 PM
  5. System Pump Down
    By Brian_UK in forum Technical Speculations
    Replies: 16
    Last Post: 25-10-2001, 10:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •