    Pressure testing with R22D ?.



    Hi,

    I want to moving two units on Diakin tri-split system containing R22d gas. This is how I plan to do it :

    1) Run new pipes to new location keeping ends covered to stop moisture entry (already done)

    2) Recover the gas into outside unit. Run sytem in cold mode for few minutes, then close liquid valve and when pressure drops to zero close gas valve and shut off sytem.

    3) Disconnect existing piping and move units.

    4) Connect new pipes to internal units and external unit. Connections made with hand flare tool not brazed.

    5) Pressure test system by filling with gas and leave overnight to see if pressure drops. I have a spare 1KG bottle of R22d - can I use this or must I use Argon / Nitrogen ?.

    6) Vac sytem and leave for few hours to see if pressure increases.

    7) Open valves. Liquid side first ?.

    8) Switch on

    Does this sound reasonable ?.
    Is there anything missing ?.
    Can I pressure test using some spare R22d and then vac system - or must I use Nitrogen/Argon ?
    The pressure guage I have has several scales for the different gases - why is this ?.

    thanks



  2. #2
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Pressure testing with R22D ?.

    Quote Originally Posted by stephengrenfell View Post
    Hi,



    5) Pressure test system by filling with gas and leave overnight to see if pressure drops. I have a spare 1KG bottle of R22d - can I use this or must I use Argon / Nitrogen ?.

    6) Vac sytem and leave for few hours to see if pressure increases.

    Does this sound reasonable ?.
    Is there anything missing ?.
    Can I pressure test using some spare R22d and then vac system - or must I use Nitrogen/Argon ?
    The pressure guage I have has several scales for the different gases - why is this ?.

    thanks
    at least 5 points in your post leave me thinking that you really should not be taking this job on board

  3. #3
    Join Date
    Jun 2009
    Location
    France
    Posts
    7
    Rep Power
    0

    Re: Pressure testing with R22D ?.

    Quote Originally Posted by stephengrenfell View Post
    Hi,

    I want to moving two units on Diakin tri-split system containing R22d gas. This is how I plan to do it :

    1) Run new pipes to new location keeping ends covered to stop moisture entry (already done)

    2) Recover the gas into outside unit. Run sytem in cold mode for few minutes, then close liquid valve and when pressure drops to zero close gas valve and shut off sytem.

    3) Disconnect existing piping and move units.

    4) Connect new pipes to internal units and external unit. Connections made with hand flare tool not brazed.

    5) Pressure test system by filling with gas and leave overnight to see if pressure drops. I have a spare 1KG bottle of R22d - can I use this or must I use Argon / Nitrogen ?.

    6) Vac sytem and leave for few hours to see if pressure increases.

    7) Open valves. Liquid side first ?.

    8) Switch on

    Does this sound reasonable ?.
    Is there anything missing ?.
    Can I pressure test using some spare R22d and then vac system - or must I use Nitrogen/Argon ?
    The pressure guage I have has several scales for the different gases - why is this ?.

    thanks

    the last line of my post sounds a bit daft. What I meant was why does the pressure guage have different zero point for the different gases (for example zero on the R22d scale is at about 4 on the bar scale.

    Thanks

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pressure testing with R22D ?.

    6 rasons why you should not be doing this work

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure testing with R22D ?.

    Sir, you will be breaking EU Law, contact an air conditioning company to do the work safely/legally.

    Do NOT use refrigerant for pressure testing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Pressure testing
    By eggman08.2008 in forum Air Conditioning
    Replies: 12
    Last Post: 10-07-2008, 07:04 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. OFN Pressure testing hoses.
    By Teknicool in forum Trouble Shooting
    Replies: 7
    Last Post: 08-07-2007, 11:41 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •