    Lightbulb York Chiller Fault



    Hi I have A York Chiller Liquid Screw Type:

    After starting when converting in delta the machine trip and on diplay status giving error star delat transit fault.after resting machine start agian after this process chiller agin trip what is the troublshooting point how to indentify the fault
    and why phase sequence meter is used in chiller?
    thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: York Chiller Fault

    Did someone else done some repairs on chiller before you arrived?

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: York Chiller Fault

    Screw compressors need right phase sequence, therefore all decent machines are provided with a relay that controls supply.
    Check:

    motor's windings' continuity,

    fuses,

    voltages, phase sequences everywhere,

    whether all power commutations have been done right - in motor's contact box, and on contactors,

    check whether all contacts close,
    whether contactors'coils are good: simply take off leads to motor, switch on, and test how they close.

    Also, maybe the supply is poor and voltage at start drops too low.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: York Chiller Fault

    it could just be an auxillary relay not making, also the auxillaries on older models were well known for "bouncing" which breaks the circuit for a split second and trips the chiller.

    al

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: York Chiller Fault

    Hopefully the test with motor leads off will evince it.

  6. #6
    kifayat's Avatar
    kifayat Guest

    Lightbulb Re: York Chiller Fault

    After emoving the fault star-delta trasit fault a new fault arises
    in status--------EMS/MP CUT OUT
    fault
    whats its mean?

  7. #7
    kifayat's Avatar
    kifayat Guest

    Lightbulb Re: York Chiller Fault

    cONTROL CIRCUIT DIAGRAME AND CIRCUIT DIAGRAME NEDEED

    MILLINIUM YORK LIQUID CHILLING SYSTEM
    MODEL NO YCW S80SC50C
    RATED CAPICITY 253KW
    DESGIN PRESSURE FOR SYSTEM 2.5 MPA
    REFREGERANT R22
    VOLTS -PHASE -HZ 390- 3 - 50

  8. #8
    Md.Anis Mondol's Avatar
    Md.Anis Mondol Guest

    Re: York Chiller Fault

    Good afternoon,I am glad for your member.

    York chiller
    Model:YK EB EB H5 5C OE.
    Fault : Oil Low differential pressure.

    Work: After maintenance we are try to run this chiller but when switching then (after 50 seconds) showing above fault.

    Also showing in Oil Sump parameter:-
    oil pressure 115 kpaD
    oil sump temperature 50 deg. cel.
    pump oil pressure (HOP) 565 kpaD
    sump oil pressure (LOP) 513 kpaD.

    Please help us.

    Thanking you
    Anis.

  9. #9
    kifayat's Avatar
    kifayat Guest

    Lightbulb Re: York Chiller Fault

    After emoving the fault star-delta trasit fault a new fault arises
    in status--------EMS/MP CUT OUT
    fault
    whats its mean?

    plz also cONTROL CIRCUIT DIAGRAME AND CIRCUIT DIAGRAME NEDEED

    MILLINIUM YORK LIQUID CHILLING SYSTEM
    MODEL NO YCW S80SC50C
    RATED CAPICITY 253KW
    DESGIN PRESSURE FOR SYSTEM 2.5 MPA
    REFREGERANT R22
    VOLTS -PHASE -HZ 390- 3 - 50

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. YORK YAEP recip chiller fault
    By chiller1 in forum Trouble Shooting
    Replies: 8
    Last Post: 04-06-2010, 10:41 AM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Replies: 3
    Last Post: 22-12-2008, 08:13 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •