    Q about superheat in evaporators



    Hi, all,

    the situation: we have to choose evaporator for cold room.
    Evap.temp. is -10 Grad C. Program needs superheat - I can input 4.6 K. Is it good value? Or better to use 3 K?

    Thanks for your answer!

    Andrew



  2. #2
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Q about superheat in evaporators

    4.5 K - good. But may be 3 K is better?

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Q about superheat in evaporators

    Will not give a diffrence that you can measure.
    3K is too small for a normal TEV.
    Chose 4 to 6 or 4.512223
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Q about superheat in evaporators

    What does it mean - "TEV"?

  5. #5
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Q about superheat in evaporators

    Thanks for translation - I use German language (and Russian).

    Bot instead thermostatic EV we can use electronic EV. In this case we get - I begin to understand - we can use smaller evaporator. And save money!

  6. #6
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Q about superheat in evaporators

    Yeah! Agree!

    thanks for the discussions - I am electrical engineer, but I work in refrigeration field. And I try to understand what does it mean - superheat etc.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Q about superheat in evaporators

    Very fruitful discussion

    Chemi

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Q about superheat in evaporators

    Hi
    small superheats are nice, but wrecked compressors are not. I would tend to go for a say 5K superheats, possibly higher, less posibility of hunting at low loading and less posibility of liquid carryover. If you want a fully flooded evaporator, buy one and the suction vessel to go with it, that is the most effecient plant. If you use direct expansion be prepared to accept less that book superheat for the sake of relyable plant.
    Kind Regards. Andy.

  9. #9
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24

    Re: Q about superheat in evaporators

    Quote Originally Posted by Marc O'Brien
    Thermal Expansion Valve
    Far too Alco sounding... or Emerson Climate Technologies Flow Control Division as they are now currently known. "Thermal Expansion Valve" is an Alco tradename.

    Thermostatic Expansion Valve is the generic description.
    Prof Sporlan

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  3. 1 Tev 2 Evaporators
    By Renato RR in forum Technical Discussions
    Replies: 14
    Last Post: 18-11-2009, 02:58 PM
  4. opens on rise of outlet
    By subzero*psia in forum Commercial
    Replies: 24
    Last Post: 01-03-2008, 10:46 AM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •