    Hi guys
    I have a CRC reach in cooler The system has a leak. I want to change out the compressor.(Afraid it sucked in contaminents) What would you change the system to. Temp Im looking for is 36 to 40 degrees F. What should I flush the system with. Thank you ahead of time
    Dec 2008
    564
    Re: R12 replacement
    R134a may be suitable, it should run on similar pressure to R12. There is a limited choice for flushing, especially if this is a capillary system. It may be best to purge with OFN to get any remaining contaminents out. Once you have purged a couple of times, then fit the new compressor, fit a liquid line drier and leak test, then give the system a good vaccing out and charge with R134a using the manufacturers charge weight as a guide. Run the unit on test and trim the gas charge if necessary.
    3,853
    Re: R12 replacement
    I would use a drop in replacement for R12 instead of R134a, such as R49/R413A as it will work better with any residual mineral oil that is in the system from the old compressor. Charge weight is typicaly 80/90% that of the original R12 charge but you will need to watch it run down to set temp a few time to adjust the charge for best operation.
    As Hyperion says, a good vac and a new drier, i might be tempeted to put one in the suction too if there is a lot of contaminants in the system.
    Let us know how it goes
    Mar 2010
    64
    7
    Re: R12 replacement
    I may put in hot shot does that take 80-90 pct charge also?
    Thank you
    One Man's Avatar
    One Man Guest
    Re: R12 replacement
    Yes sir Randy. I actually just charged an old R-12 system with Hot Shot today. The charging chart says tha you need 80% of a standard charge with R-414b (Hot Shot). The system is moving heat wonderfully and I'm pretty pleased.
    Split Croatia
    6,151
    Re: R12 replacement
    DuPont refrigerant _Replacement_Guide.pdf
    http://www.mediafire.com/?z2ymtfykw2y
  1. R22 replacement
    By brad__34 in forum Refrigerants
    Last Post: 04-06-2010, 09:06 PM
  2. Replacement for R403b
    By fridgability in forum Refrigerants
    Last Post: 20-08-2009, 03:36 PM
  3. Replacement Chiller Barrel Selection
    By archibaldtuttle in forum Air Conditioning
    Last Post: 09-06-2009, 08:09 PM
  4. Replacement Screw Compressors
    By dkemper in forum Technical Discussions
    Last Post: 13-10-2007, 07:22 PM
  5. F 11 replacement for flushing
    By andrewuk in forum Refrigerants
    Last Post: 17-10-2003, 11:03 PM