    Re: Cooling Massive Heat Loads


    US Iceman,

    My experience with running single stage chambers down to -40 hasn't been too good. I can get them down there but they have almost no capacity below -20C or so. I have a 2HP system that can only handle about a 200w load below -35C. I think with the high heat load I might need to go cascade. Since I am not a cascade designer (or anything like that) I will probably have to purchase one. Cascade Tech sells them but they are not cheap dose anyone know a company that sells premade cascade refrigeration units?

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Cooling Massive Heat Loads

    This is not a typical application. It is not the same as a walk-freezer. Heat load has nothing to do with needing a cascade system.

    The use of cascade system might be required when the temperatures needed are lower than you can reasonably attain with either single stage or two stage systems. At -40°F (or -40°C) the system has to be designed to provide the required capacity at that temperature. You certainly do not need a cascade system for this temperature IMO.

    If the system you mentioned does not reach the desired temperature the system is either not designed properly or is operating outside of the design point where it was designed to operate.

    Most of the issues you mention are ones normally encountered in this type of work. They are all solvable, if approached right.
    If all else fails, ask for help.


Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  5. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •